Its easy enough to test for. There is someone on this forum who makes AC extension outlets that have the DC Blocker built in. Just use one of those and you would know if that's what it is.
08-22-12: Atmasphere
Atmasphere,
Agree....
The Agon's members username is Gbart.
Email address, sae2300@optimum.net
>>>>
Jim, wouldn’t his other “standard 15 amp” outlets, throughout the apartment, be split up between the two incoming legs? He has tried, unsuccessfully, to energize the amp from various 15 amp locations around the apartment, though it isn’t known how they are split up.
Frank
08-22-12: Metro04
Frank,
Maybe.... But not necessarily. Back in the 1970s it was not uncommon to put most of the 15 amp convenience outlets in the living room and bedrooms on the same 15 amp branch circuit. Sailcappy had a 50/50 chance the circuit/s is/are fed from the other Line.
Sailcappy could check if the receptacle/s he plugged the amp into is fed from the same Line, leg, as the dedicated circuit.
Each breaker space down each side of the panel alternates from one Line to the other.
Example Line 1, L1, is the top breaker as well as the top breaker across from it.
2nd breaker down is fed from L2 as well as the one across from it.
And so on down each side of the panel.
Glad you brought up again that Sailcappy tried other outlets in his apartment.... Those in the living room as well as bedrooms are more than likely 15 amp branch circuits fed from a 15 amp breaker....
Sailcappy, is that correct? A 15 amp breaker? IF 15 amp, during the test, did the 15 amp branch circuit breaker ever trip?
I should mention, the breakers in the panel are thermal/magnetic type breakers.
.