Isolation Transformer and Subpanel recommendations


There are many isolation transformers out there new and used. What are the best recommended 5kVA/other isolation transformers for high-end audio setups. I live in the US so I need one that would be configurable for 110/120V output. I intend to put this on my dedicated circuit after my main panel in the house. The dedicated circuit is high-quality and 20-amp/10-guage in nature; this circuit is 110/120V, not 220. I'm looking for any recommendations for units that run quiet and have high common-mode noise rejection.

Also looking for recommendations on good quality sub-panels.

Thank you in advance for the assistance!
128x128Ag insider logo xs@2xzephyr24069
Gbart....thank you very much! If memory services the Torus units have their own isolation transformers built into them so this would accomplish more than one goal at the same time. Equitech also makes a high grade all in one panel that has an isolation transformer, EMI/RFI filtering and an isolation transformer all in the same unit; don't know what this costs but it seems like there are several ways to accomplish all this that people have utilized with great success.
BTW...in talking with an audiophile who knows a hell of a lot more than I do on this, it became clear that some of my responses and my not being an electrician have caused confusion on the thread. Apologies all around for this...
Thanks to all of you who tried to help. I've pieced together (with Arnie's help) the essential points I should be chasing if I make this modification and definitely appreciate the help!
End result is better quality power to my system; the dedicated circuit, rebalancing the house panel to make the dedicated circuit the first one off the main, all other high current circuits on the other leg/phase of the house panel, good quality wiring from the main panel to the room,

all other high current circuits on the other leg/phase of the house panel,
Sometimes that can be a bad idea. Doing so can put a strain on the secondary of the utility company's power transformer. It can also put stress on the busing and breaker connecting bus ties of the main service electrical panel.

In most residential housings areas the utility power transformer is a single phase xfmr.

The single phase secondary winding is center tapped in the middle of the winding. Thus the term split phase winding.

From the xfmr secondary to your house there are 3 power conductors.
The two hot insulated conductors connect to the outer most 240V leads of the xfmr secondary winding and the center tap conductor, the intentionally Grounded Conductor, the neutral.

To cut to the chase....

NEC code requires, as well as electricians are taught, to balance out the loads across the Lines, legs, of an electrical panel as much as possible.
Example the electrician would never put the microwave, dish washer, washing machine, sump pump, known deep freezer outlet, and the gas furnace blower motor all on the same Line, leg, in the panel.

Here is how a single phase, split phase transformer works.

Theoretically, if exactly 10 amps of load is connected across line one, L1, to neutral and exactly 10 amps of load is connected across L2 and neutral, zero amps will return on the neutral conductor back to the utility xfmr.
Only the unbalanced load will return on the neutral conductor......

The two 10 amp loads are in series with one another....
The two exactly equal 10 amp series load are actually being fed by the hot 240V legs of the panel.

Any unbalanced load will return on the neutral conductor to the source, the xfmr.

Example.

Say there are 30 amps of total connected load across L1 and neutral and only 5 amps of total connected load across L2 and neutral.

25 amps will return on the neutral conductor. The remaining 5 amps of L1 will be in series with the 5 amps of L2.... Is the balanced series load dirty or clean?
.
.
If the main panel is evenly balanced within reason and a 5 Kva iso xfmr is connected across L1 and L2, fed 240V single phase balanced power then everybody is happy. Especially the utility power transformer.

What a good iso xfrm will give you is a new separately derived grounded AC power system. The wiring method used for the installation of the xfmr, the new electrical panel, and grounding will greatly determine its power quality performance.



http://openbookproject.net/electricCircuits/AC/AC_10.html#xtocid71230

it became clear that some of my responses and my not being an electrician have caused confusion on the thread. Apologies all around for this...
09-11-12: Zephyr24069
Zephyr24069,

For a layman I thought you did fine.

Asking questions is a good thing.
It is a hell of a lot cheaper to design the wiring methods that will give you the best results you are looking for than ending up with something you are not happy with.

Good example. You would be surprised how many audio enthusiast will hire an electrician to install a 5 Kva or 7 Kva xfmr and electrical panel.

Instead of configuring, paralleling, the secondary windings for 120V out they will series the 2 windings and feed the new panel with 120/240V.

Of course the audio enthusiast told the electrician to make sure all the branch circuits are fed from the same Line, leg, in the panel. So that is exactly what the electrician does.

Problem is only one winding of the two secondary windings is being used.
In other words each of the secondary windings of a 5 kva xfmr are good for a max connected load of 2.5 Kva.. (20.8 amps @120V)

By configuring, paralleling the two windings and feeding the new panel 120V the full 5Kva rating of the xfmr is available. (41.7 amps at 120V.)

The earth connection of the secondary conductor of the xfmr that will become the grounded conductor, the neutral, can also be an important factor. NEC code says it shall connect to the main grounding electrode system of the main electrical service.

Were the connection to the main grounding electrode system is connected can make the difference in how clean, free from AC noise the ground is and that of the neutral of the new separately derived grounded AC power system.....

I have only scratched the surface....

So don't be afraid to ask questions. Choose a good state licensed electrician that will set down with you and design the electrical system you want. He will know the code for your area and what the AHJ, authority having jurisdiction, will allow.

Just remember code is bare minimum safety standards. You can exceed the bare minimum standards.
Jim
Jea48: Thank you VERY much for all the additional information; I've learned a lot by starting this thread! The only word that comes to mind is "Wow!" concerning your level of knowledge. I will check with a good licensed electrician when proceeding with this next phase of system evolution. I'm currently starting to read alot on Controlled Power Systems and Topaz isolation transformers and SquareD (?) breaker boxes plus related topics. No rest for the wicked when it comes to the pursuit of great music listening experiences :-)