Hi Nick,
While there are a number of differences between the specs for the two fuses, I don't see anything all that dramatic. Although the Conquer ADL datasheet is not nearly as comprehensive as the Buss MDL datasheet.
The Conquer ADL has a nominal melting spec of 48 amps squared-seconds. The corresponding figure for the Buss MDL fuse is 62.3, which would suggest that the ADL will blow a little bit more readily. However, those are nominal (typical) figures, and each fuse can be expected to have a fairly wide tolerance (range of variation) about those numbers. Also, the specific test conditions are not indicated in the case of the Conquer fuse.
Both datasheets provide figures for min and max blow times at 200% of rated current (which would be 4 amps in this case). Those numbers are 5 seconds min and 120 seconds max, for both fuses.
"Interrupting ratings" are 100 amps at 250 VAC in both cases. Cold state resistance is spec'd a little higher in the case of the Conquer ADL fuse, but the ADL datasheet doesn't indicate what current level that is measured at, so direct comparison is iffy. And that number doesn't have much if any relevance to protection anyway.
That covers essentially all of the relevant specs that are provided in the ADL datasheet. The Buss MDL datasheet is more comprehensive, as I said, so a fully conclusive comparison can't be drawn. And who knows how accurate the specs are? But based on the info that IS provided on the ADL fuse I don't see any worrisome differences.
Best regards,
-- Al
While there are a number of differences between the specs for the two fuses, I don't see anything all that dramatic. Although the Conquer ADL datasheet is not nearly as comprehensive as the Buss MDL datasheet.
The Conquer ADL has a nominal melting spec of 48 amps squared-seconds. The corresponding figure for the Buss MDL fuse is 62.3, which would suggest that the ADL will blow a little bit more readily. However, those are nominal (typical) figures, and each fuse can be expected to have a fairly wide tolerance (range of variation) about those numbers. Also, the specific test conditions are not indicated in the case of the Conquer fuse.
Both datasheets provide figures for min and max blow times at 200% of rated current (which would be 4 amps in this case). Those numbers are 5 seconds min and 120 seconds max, for both fuses.
"Interrupting ratings" are 100 amps at 250 VAC in both cases. Cold state resistance is spec'd a little higher in the case of the Conquer ADL fuse, but the ADL datasheet doesn't indicate what current level that is measured at, so direct comparison is iffy. And that number doesn't have much if any relevance to protection anyway.
That covers essentially all of the relevant specs that are provided in the ADL datasheet. The Buss MDL datasheet is more comprehensive, as I said, so a fully conclusive comparison can't be drawn. And who knows how accurate the specs are? But based on the info that IS provided on the ADL fuse I don't see any worrisome differences.
Best regards,
-- Al