how to run a 230 volt line from my panel??


I am getting a piece of equipment from europe that is set for 230v- I called the manufacturer and they said it can not be rewired to 110 I should simply run a 230 line= i already have 12 gauge wire ran to the stereo room- Is it just a matter of getting a 20 amp 230v breaker for my elec. panel-
Can i use the outlets I have now and a USA type power cord or what do I need to do?- thanks
fluffers
BTW: the site I listed shows the configurations of IEC plugs, 125V(C-14) vs 230/250V(C-20). Note that the contacts of your expected 230V component's connector(chassis end) will be(most likely) horizontal, the ones on your 125V cord are vertical. Of course; you can change the IEC outlet, on your chassis or the IEC female, on your cord(http://www.vhaudio.com/connectors-ac.html#OyaideIEC).
First off... Is this a house, townhouse or condo? Seen the latter 2 with 208V, sort of 2/3 phase.

Second... What kind of equipment? Turntable, CDP, preamp or amp? If it's low power consumption, a step-up transformer (Topaz, Phoenix ...) might be easiest, cheapest and safest solution. Sometimes not the quietest. As far as I've seen, only a few turnatables are sensitive going from 50 to 60 Hz.
this is a cdplayer- running in a house- Since I already have the lines run to the room and room in the box it seems the prudent way to go-yes I was planning to ecut the ends of my current power cord and buy the correct connections for a 20 amp wall socket-p does this seem to make sense to everyone or am i missing something- thanks for all the advice--
Europe uses 50 Hz current rather than 60 Hz in North America. I would assume that most transformers nowadays can handle both, but it would be worth confirming.

Michael
Just for every ones information.

NEC 2011
Article 210.6 (A)
Occupancy Limitation. In dwelling units, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply,

(2) Cord-and-plug loads 1440 Va, nominal, or less or less than 1/4 HP.

Fluffers,

It's a CDP.... Power consumption is next to nothing. JMO buy a small step-up transformer.

Also worth mentioning the 230V CDP was designed to be fed from a 230V AC grounded power system. A hot, (the ungrounded conductor), and a neutral, (the grounded conductor).

Good chance only one line, the hot conductor is fused inside the CDP.
Good chance the power switch is a single pole and only breaks one line, the hot conductor.
.