Most, if not all qualified electricians will calculate the load of the circuits and split them at the panel to keep the house loads approximately equal so as to not overload one side.
05-13-13: Minorl
I would bet all of Bifwynne audio equipment loads added together would not total more than 8 to 10 amps continuous load, if that. Most hair dryers pulls more current than that.
It is an established best practice that when audio equipment is connected together by ICs the AC power feeding the equipment should be fed from the same Line, leg, of the same electrical panel.
The worst thing that Bifwynne could do is have an electrician install a 120/240V multi wire branch circuit. (2 hot conductors with a common shared neutral conductor.) What better way to couple the power supply of digital equipment to the power supply of analog.
Bifwynne wants dedicated branch circuits installed, not separate circuits.
Split Single Phase electrical service is most commonly found in residences and smaller commercial buildings,http://www.exactpower.com/elite/assets/pdfs/theTRUTH.pdf
and is commonly used to feed AV equipment. One key advantage that single phase has over three phase
is that while harmonic currents are still present, it is not possible for the “triplen” components to add in the
neutral. In addition, use of split single phase can result in at least a 6dB reduction in noise floor as compared
to three phase if the capacitances of the connected equipment are relatively well balanced. However, any
leakage currents on the safety ground wires of split single phase load circuits fed by different phase legs will
add together due to the 240V potential difference.
.