Coxhaus,
Just curious have you ever checked if the outputs of your three isolation transformers are in phase with one another?
Simple test.
Using a volt meter/multi meter set the meter to AC auto or for AC over 300Vac.
Insert one test lead probe in the hot contact, small slot, of a receptacle fed from one transformer and the other test lead probe into the hot, small slot, of a receptacle fed from one of the other transformers.
If in phase you will measure 0 Vac nominal. If out of phase you will measure 240Vac nominal. Check each hot to hot contact from each receptacle fed from each transformer.
If out of phase the 240Vac nominal is lethal real potential power, not phantom power.
You want the outputs of the isolation transformers to be in phase with one another where audio equipment is connected together by ICs.
.
Just curious have you ever checked if the outputs of your three isolation transformers are in phase with one another?
Simple test.
Using a volt meter/multi meter set the meter to AC auto or for AC over 300Vac.
Insert one test lead probe in the hot contact, small slot, of a receptacle fed from one transformer and the other test lead probe into the hot, small slot, of a receptacle fed from one of the other transformers.
If in phase you will measure 0 Vac nominal. If out of phase you will measure 240Vac nominal. Check each hot to hot contact from each receptacle fed from each transformer.
If out of phase the 240Vac nominal is lethal real potential power, not phantom power.
You want the outputs of the isolation transformers to be in phase with one another where audio equipment is connected together by ICs.
.