tomiiv30 OP32 posts01-21-2019 2:05pm
It is one rod that he installed in the ground that is few feet away from the outside meter/box, the other rod was installed form the electrical company, it was already there, that’s why I thought he did 2.
One of the 20 amp outlet is grounded to the inside of the panel.
The other 20 amp outlet is grounded directly from the outlet to the outside rod with a clamp that is attached to the rod itself, I saw that with my own eyes. It is a straight wire that goes from the outlet to the outside and has nothing to do with the inside panel or anything else in the house.
The other 20 amp outlet is grounded directly from the outlet to the outside rod with a clamp that is attached to the rod itself, I saw that with my own eyes. It is a straight wire that goes from the outlet to the outside and has nothing to do with the inside panel or anything else in the house.
YOU are going to have to find out exactly what the guy did!
Do you feel comfortable pulling the wall duplex outlet from the wall box for a look to see exactly what the guy did?
IF yes.
Turn off the breaker at the electrical panel that feeds the outlet. Plug a lamp into the outlet to make sure 100% the power is off. 100%! To verify the lamp is turned on and the bulb is good plug it into a live outlet. Lamp bulb should light.
Pull off the outlet cover plate.
Remove the two 6/32 screws that hold the outlet to the wall box.
Pull the receptacle outlet straight out from the box far enough to look at the wires that are connected to the receptacle as well as those that enter the box.
Is the box metal or plastic?
As for the branch circuit wiring that enters the box, I believe you said in an earlier post it is Romex. You should see a black insulated wire (Hot), a white insulated wire (Neutral), and a bare copper wire, the safety equipment grounding conductor.WHERE IS THE BARE WIRE CONNECTED TO???
*****Examples:
1) ** IS THE BARE WIRE connected to the ground wire that comes in from the outside isolated ground rod along with a short wire, pigtail, that connects to the green equipment ground screw on the isolated grounding type receptacle outlet? IF the box is metal the box must also be bonded, connected, to the ground wires connection with another pigtail. All connections should be under one wire connector, example a wire nut. IF this is what you have then the guy wired the grounding per NEC Code as an Auxiliary Grounding Electrode. Lightning loves Auxiliary Grounding Electrodes!
NOT NEC compliant!
2) ** IF a metal wall box was used the Romex cable bare copper safety equipment grounding conductor is bonded, connected, to the metal box ONLY. Period.... IF the box is plastic the Romex Cable bare equipment ground wire is not connected to anything. It is just pushed back inside the box.
The ground wire that enters the wall box from the outside isolated ground rod connects to the green color ground screw on the isolated grounding type receptacle ONLY. Period....
If this is the way the guy wired the grounding it is dangerous and could cause an electrical shock hazard or worse possible electrocution in the event of a hot to chassis ground fault event.
Also note you do not have a low resistance path for ground fault current to return to the source, the electrical service neutral conductor, in the event of a hot to chassis fault. This would also include anything plugged into the wall outlet. That includes the power cord feeding any equipment. Cut to the case, the breaker in the electrical panel that protects the branch circuit wiring will never trip open in the event of a ground fault event.
//
As for your power quality problem there is always a solution. It may require you hiring a certified credited power quality testing company. In my area they charge around $125 an hour. In your case the tech would be there about an hour or so..... He/she will have the test equipment needed to find your power quality problem. If it is coming in from outside your home the testing company will provide you with the necessary test reports to show to your utility power company. If it is inside your home the power quality company will identify the problem. If it is structure electrical wiring or fixed electrical equipment a licensed electrician will be required to make the repairs. In most cases the power quality company will recommend an electrical contractor company they use.
Jim
.