How far away is the main panel from your listening room? If it’s more than 50 feet then it pays to put in a subpanel since a branch circuit of that distance will have a high voltage drop (3 volts with #12 and 1.8 volts with #10 at a 15-amp peak draw).
If distance is not an issue, use 10/3 romex because the wires are spiraled and that reduces common mode noise. Cut the bare grounding conductor and use the red wire for ground (tape it green where exposed, of course). Also, use the clamps under the screw of the receptacle for #10 wire instead of looping it around the screw. And use 10/3 from the subpanel to the receptacle also.
If distance is not an issue, use 10/3 romex because the wires are spiraled and that reduces common mode noise. Cut the bare grounding conductor and use the red wire for ground (tape it green where exposed, of course). Also, use the clamps under the screw of the receptacle for #10 wire instead of looping it around the screw. And use 10/3 from the subpanel to the receptacle also.