Whart,
Not all electrical inspectors are created equal. With that said the one you are dealing with, for your area, usually has the final say.
The out building needs to be considered a commercial space and not a residential dwelling unit to meet NEC code Article 647.
Use the word commercial space when talking with the AHJ, Authority Having Jurisdiction, when getting an electrical permit. When the inspector comes out to inspect the installation make sure when referring to the out building, refer to the space as a commercial space and not as a residential habitable space. There is a big difference between the two in the eyes of NEC code.
One other thing worth noting is zoning. Is the area you are buying the house with the out building zoned residential only or residential/light commercial?
[Quote] from Link below:
ARTICLE 647 -- SENSITIVE ELECTRONIC EQUIPMENT
647.1 Scope. This article covers the installation and wiring of separately derived systems operating at 120 volts line-to-line and 60 volts to ground for sensitive electronic equipment.
647.3 General. Use of a separately derived 120-volt single-phase 3-wire system with 60 volts on each of two ungrounded conductors to a grounded neutral conductor shall be permitted for the purpose of reducing objectionable noise in sensitive electronic equipment locations provided that the following conditions apply.
(1) The system is installed only in commercial or industrial occupancies.
(2) The system's use is restricted to areas under close supervision by qualified personnel.
(3) All of the requirements in 647.4 through 647.8 are met.
647.4 Wiring Methods.
http://www.equitech.com/support/647.html
.
Not all electrical inspectors are created equal. With that said the one you are dealing with, for your area, usually has the final say.
The out building needs to be considered a commercial space and not a residential dwelling unit to meet NEC code Article 647.
Use the word commercial space when talking with the AHJ, Authority Having Jurisdiction, when getting an electrical permit. When the inspector comes out to inspect the installation make sure when referring to the out building, refer to the space as a commercial space and not as a residential habitable space. There is a big difference between the two in the eyes of NEC code.
One other thing worth noting is zoning. Is the area you are buying the house with the out building zoned residential only or residential/light commercial?
[Quote] from Link below:
ARTICLE 647 -- SENSITIVE ELECTRONIC EQUIPMENT
647.1 Scope. This article covers the installation and wiring of separately derived systems operating at 120 volts line-to-line and 60 volts to ground for sensitive electronic equipment.
647.3 General. Use of a separately derived 120-volt single-phase 3-wire system with 60 volts on each of two ungrounded conductors to a grounded neutral conductor shall be permitted for the purpose of reducing objectionable noise in sensitive electronic equipment locations provided that the following conditions apply.
(1) The system is installed only in commercial or industrial occupancies.
(2) The system's use is restricted to areas under close supervision by qualified personnel.
(3) All of the requirements in 647.4 through 647.8 are met.
647.4 Wiring Methods.
http://www.equitech.com/support/647.html
.