Dedicated Lines - Sub panel or no?


Hi folks,

In a few months time I will be moving to a new home, where a spare bedroom and an understanding wife will enable me to enjoy the luxury of a dedicated listening room.

The first thing that comes to mind is installing 4 dedicated 20A lines. The breaker panel is on the ground floor, the room is on the 3rd.

I'm wondering which is better:

-to run all four lines from the breaker box all the way to the wall outlets,

-or install a sub-panel (is that the right term?) in the room, and use a single, very heavy guage line from the breaker box to the subpanel, then run 4 short lengths of 10 or 12 gauge from the subpanel to the outlets.

Thanks in advance for your advice

Kind Regards
Mick
128x128mickey_sg
FWIW, I went the sub panel route. That allowed for a very large gauge wire for the long run. Then I used robotic control cable(exceptionally high quality shielded wire from Germany used for the most sensitive robotic applications) for the shorter runs. Then used isolation & conditioning for each run. It worked very well.
As a cost-no-object solution, Psacanli, you got it.
For the rest of us, a good dedicated line or 2 will have to do. I suspect that a good dedicated line is well over half the battle. For a room add-on, I'd LIKE to use a sub-panel.
I used to be able the flicker the house lights with my Carver Cube....years ago. But now, with 2x the power and a dedicated line, I can do no such thing.
If I lived where there were lightning storms, I'd also have a whole-house lightning arrest system.
Go with the sub panel, as it will allow room for potential add on later.
Never know how many lines the future may need :-)
I use a subpanel but my requirements are unique.

I have 3 amplifiers (2400W combined) for stereo. Much of that in class A.

I supply a large step-down transformer with 240V for balanced AC output for 2 of the amps.

A TVC line stage provides galvanic isolation between the CDP and amps. There can be different voltage between legs which can cause noise but that has not been an issue in my case.

I have the subpanel/transformer located in a closet directly behind the equipment.

The origional main panel is obsolete and breakers are no longer available.

I was able to run 6/3 wire through the crawlspace.

I rent.
I think the comment by Liquid Hi Fi is very valid and should be a major factor in your decision. You provide a foundation for future upgrades in vital power supply area.