jea48,
By re-grounding- I removed the old grounding connectors, (both phone and CATV) at the grounding rod and at the exterior (outside) cable junction box. I Cleaned the stake with a wire wheel, (to remove rust or oxidation) and reinstalled new 12 awg solid ground wire and connectors.
I still had the (((hum))). With the system on and the volumn at a reasonable level, I disconnected the coax from the cable box and the (((hum))) disappeared.
This was my particular situation. I hope it helps.
nutty,
Thank you for your response.
The ground rod you speak of. Did you notice any other ground wires that were connected to it? Like a larger #6 bare or stranded copper wire?
Just a guess the ground rod was originally installed for the phone and later when CATV was installed the CATV installer used the same ground rod.
Unless the ground rod is fairly close to where the main electrical service of the house is located I doubt the ground rod for the phone or CATV is connected by at least a #6 copper ground wire to the main grounding system of the electrical service.
Many people think, including communication provider companies installers, a separate isolated ground rod is all that is needed to effectively ground their systems to mother earth. It is not though. Electrical safety codes require the systems shall be bonded, connected, to the main grounding system of the electrical service. The main reason all ground rods need to be tied, connected, together is for lightning. You also want all electrical systems grounding connected to one common ground.