Outlet is "Open Ground" - Is There Still a Safe Way to Connect to My Audio Gear?
So typically from a wall power outlet runs a very short Nordost Power Cable to Nordost's Qb8 "power strip," and then a loom of Nordost Power Cables to my vinyl audio set up All the Nordost cables were bought used and sound great. Having just moved and set up everything in a new room, the nearest power outlet is "Open Ground"(!) Without moving everything around to fit the main Power Cable length to a "Grounded" outlet, please is there a safe and best sounding way to still use this outlet to power everything? Thanks! :-)
You should get the grounding issue fixed, but the only "fix" for this I know of is to use a GFCI outlet and label it with the sticky labels that say "No Equipment Ground."
However, not ideal and most surge protectors won’t work correctly in this state. This will however save your ass in case of a short to the chassis.
I have had to replace several duplex outlets over the years. Definitely two wire open ground. There is an addition on the house, built in the 1980's. Those outlets do have the typical green grounding cable, but the breaker box (since replaced and upgraded) was still from the 1950's and didn't have provisions for actual grounded outlets, anywhere in the house.
I don't have access to the model number of the Panamax surge protector, but it's a fairly low end model. All I know is when the amp was plugged directly to the mains, it's metal front cover conveyed some minor current flow and when plugged into the Panamax, it was resolved.
I am not in a position to rewire my entire home either DIY or via a paid professional. I also don't own equipment anywhere near true audiophile or reference level cost or performance.
You should get the grounding issue fixed, but the only "fix" for this I know of is to use a GFCI outlet and label it with the sticky labels that say "No Equipment Ground."
This is what NEC code calls for. Had to scroll too far down for to finally reach the correct answer. You can also replace the first receptacle on the circuit with the GFCI and attach the downstream receptacles to "load" and label them per above. This will ensure each receptacle on the circuit is protected by the single GFCI. Or place the GFCI solely on the receptacle in question.
This is what NEC code calls for. Had to scroll too far down for to finally reach the correct answer. You can also replace the first receptacle on the circuit with the GFCI and attach the downstream receptacles to "load" and label them per above. This will ensure each receptacle on the circuit is protected by the single GFCI. Or place the GFCI solely on the receptacle in question.
Check my post on
FYI, 2020 NEC 406.4 (D) (2) (a) says an old two wire receptacle can be replaced with a new 2 wire receptacle when there is not an equipment ground present.
Would a GFCI outlet be better for his situation feeding his audio equipment? Yes... If the box is deep enough... IMO a new 20A dedicated branch circuit would be better. My bet the OP will hear a difference, for the better.
Back in the old days some of the steel boxes used for wall outlets may not be deep enough for the installation of a GFCI duplex receptacle. (He has 4 cloth covered rubber conductors in the box as well.) The electrician he hires will check the box for fit. I am sure the electrician will know what he can do.
FWIW...
There are other options to add GFCI protection to the 2 wire convenience outlet branch circuit. One, is to install a GFCI breaker in the electrical panel. (providing the branch circuit is not part of a multiwire branch circuit.) That would also allow a 3 wire grounding type receptacle to be installed for his audio system. (Label would be required on the outlet cover plate.) Just a guess, more than likely all the duplex outlets on the 2 wire branch circuit have 3 wire grounding type outlets installed on the 2 wire circuit. Just a guess there may be some ceiling lighting on the circuit as well.
What the OP should not do himself is mess with the old branch circuit wiring. Especially if the insulation on the wires is old cloth covered rubber.
You must have a verified phone number and physical address in order to post in the Audiogon Forums. Please return to Audiogon.com and complete this step. If you have any questions please contact Support.