Whart, glad to hear you will not be using a separate equipment grounding conductor and ground rods for the sub panel that does not connect back to the main electrical service panel grounding electrode system.
====
>>"My electrician has installed a separate subpanel for the audio system which is 'upstream' even of the main breaker panel in the house."<<
>>>>>>>>>>>>
Just curious how did the electrician do this? Did he tap into the Hot conductor/s ahead of the main breaker, of the main service electrical panel? What size is the main 2 pole breaker, 100 amp, 200 amp? Did he install a new breaker and enclosure at this tapped location to protect the feeder that runs to the new sub panel? How did he connect to the neutral conductor ahead of the main service panel? How far is the sub panel from the main electrical panel? What size of wire did he install to the new sub panel? How many conductors, wires?
====
>>"My electrician has installed a separate subpanel for the audio system which is 'upstream' even of the main breaker panel in the house."<<
>>>>>>>>>>>>
Just curious how did the electrician do this? Did he tap into the Hot conductor/s ahead of the main breaker, of the main service electrical panel? What size is the main 2 pole breaker, 100 amp, 200 amp? Did he install a new breaker and enclosure at this tapped location to protect the feeder that runs to the new sub panel? How did he connect to the neutral conductor ahead of the main service panel? How far is the sub panel from the main electrical panel? What size of wire did he install to the new sub panel? How many conductors, wires?