Frequently, when I switch light-switches on, I burn out light bulbs and at times a breaker jumps.

I am preparing to purchase new tube amps, (I currently have a ss amp). I am worried that these surges may cause damage to the new tube gear.

I live in a newly constructed building (4yrs old) which is shared with 5 other tenants. Throughout the building in the hallways and such, there are always burnt out bulbs. Bulbs last less than 6 month on average (incandescent, halogen and fluorescent)

This seems to occur randomly, last time was in the evening 8pm, whereas the time before it was at 4:45 am.

Need I be worried?
What can be done to solve the root of the problem?
What can be done to mitigate the risks? I already have a surge protector but I only have my Pre-amp, TT & TV plugged into it. I find the amp sounds better straight in the wall.
nick_sr
Nice explanation, Jim. Thanks!

So if he has a 3V differential between ac neutral and ac safety ground at the particular outlet he measured, let's make the following rough assumptions:

-- 100 feet of wiring from the outlet to where those two lines are bonded together at the service panel.

-- Negligible current flowing through the safety ground wiring.

-- Wire resistance of 1.6 ohms per thousand feet (corresponding approximately to 12 gauge wire). Which would mean 0.16 ohms for 100 feet.

That would mean, if the resistance through the path is what it should be, that he has 3/0.16 = 18.75 amps flowing through the neutral wiring on that line.

Sounds kind of high, suggesting that perhaps the resistance is higher than it should be somewhere in the neutral run.

If so, meaning that losses in the hot side of the wiring are small compared to the losses in the neutral run, the voltage at the service panel for that line would be the 124.5 measured at the outlet + 3 = 127.5 volts.

And if not (if connection integrity is good for all of the neutral path between service panel and outlet), there is presumably also a 3V drop in the hot side of the wiring. That would mean that the voltage at the service panel for that line would be the 124.5 measured at the outlet + 3 x 2 = 130.5 volts.

In either case, these numbers provide added credence to the possibility you have suggested.

Does that all sound right?

Regards,
-- Al
Al, (Jea48 I answer you below)

Here are the readings from throughout the day:
1pm: 124.5v
6pm: 123.0v
10pm: 120.0v
12am: 124.0v
5am: 125.3v
9am: 124.3v

Given the above, it would reasonable to expect that the voltage could reach above 126v.

Jea48,

...if any incandescent light bulbs suddenly get brighter than normal...

The only time the lights dim is when my wife switches on the kettle. The kettle is plugged into the same breaker as the plug that the lights in the main living area are connected to.

If I take a reading on that plug the voltage drop is from 123.8 to 110. (measured across both vertical slots). However, if I measure from the short vertical to the ground then it reads 116v. If I turn off the kettle the reading goes back to the 123.8.

In regards, to other big consumers, I have regular fridge a wine fridge, dishwaser etc... I have never noticed a diming or brightning of the lights as these appliance switch on of off. I live in open concept condo, so I can hear when these appliance switch on and off.

Breaking News!!! As i am writing this, my surge protector just tripped, I measured the voltage and it is at 126.5v.

I guess I should contact my utility company!

One last point regarding my fellow tennants, the bulbs in the hallway are constantly burning out. I have not explicitly raised this issue with any of the neighbours but I will bring it up in our next condo meeting. I am quite sure that this is shared problem.

Thanks for the help it is greatly appreciated!
The only time the lights dim is when my wife switches on the kettle. The kettle is plugged into the same breaker as the plug that the lights in the main living area are connected to. If I take a reading on that plug the voltage drop is from 123.8 to 110. (measured across both vertical slots). However, if I measure from the short vertical to the ground then it reads 116v. If I turn off the kettle the reading goes back to the 123.8.

Nick -- How many watts does the kettle consume? That should be indicated on a label somewhere on it.

Regards,
-- Al
Nick -- How many watts does the kettle consume? That should be indicated on a label somewhere on it.

1500 watts
The only time the lights dim is when my wife switches on the kettle (1500 watts). The kettle is plugged into the same breaker as the plug that the lights in the main living area are connected to. If I take a reading on that plug the voltage drop is from 123.8 to 110. (measured across both vertical slots). However, if I measure from the short vertical to the ground then it reads 116v. If I turn off the kettle the reading goes back to the 123.8.

Jim, it sounds like he's got a bit more than about 1/2 ohm of resistance between the service panel and the outlet, in each of the two runs (hot and neutral). Seems a little high, unless the runs are unusually long.

But in any event, that would mean that all of the voltage readings Nick reported (measured at the outlets) are probably understating the voltages at the service panel, by around 1.1 volts per amp of current draw. And since those measurements are highish to begin with, it sounds like something really is amiss on other side (the outside) of the service panel.

So I agree that a call to the power company definitely seems warranted.

Regards,
-- Al