Al, (Jea48 I answer you below)
Here are the readings from throughout the day:
1pm: 124.5v
6pm: 123.0v
10pm: 120.0v
12am: 124.0v
5am: 125.3v
9am: 124.3v
Given the above, it would reasonable to expect that the voltage could reach above 126v.
Jea48,
The only time the lights dim is when my wife switches on the kettle. The kettle is plugged into the same breaker as the plug that the lights in the main living area are connected to.
If I take a reading on that plug the voltage drop is from 123.8 to 110. (measured across both vertical slots). However, if I measure from the short vertical to the ground then it reads 116v. If I turn off the kettle the reading goes back to the 123.8.
In regards, to other big consumers, I have regular fridge a wine fridge, dishwaser etc... I have never noticed a diming or brightning of the lights as these appliance switch on of off. I live in open concept condo, so I can hear when these appliance switch on and off.
Breaking News!!! As i am writing this, my surge protector just tripped, I measured the voltage and it is at 126.5v.
I guess I should contact my utility company!
One last point regarding my fellow tennants, the bulbs in the hallway are constantly burning out. I have not explicitly raised this issue with any of the neighbours but I will bring it up in our next condo meeting. I am quite sure that this is shared problem.
Thanks for the help it is greatly appreciated!
Here are the readings from throughout the day:
1pm: 124.5v
6pm: 123.0v
10pm: 120.0v
12am: 124.0v
5am: 125.3v
9am: 124.3v
Given the above, it would reasonable to expect that the voltage could reach above 126v.
Jea48,
...if any incandescent light bulbs suddenly get brighter than normal...
The only time the lights dim is when my wife switches on the kettle. The kettle is plugged into the same breaker as the plug that the lights in the main living area are connected to.
If I take a reading on that plug the voltage drop is from 123.8 to 110. (measured across both vertical slots). However, if I measure from the short vertical to the ground then it reads 116v. If I turn off the kettle the reading goes back to the 123.8.
In regards, to other big consumers, I have regular fridge a wine fridge, dishwaser etc... I have never noticed a diming or brightning of the lights as these appliance switch on of off. I live in open concept condo, so I can hear when these appliance switch on and off.
Breaking News!!! As i am writing this, my surge protector just tripped, I measured the voltage and it is at 126.5v.
I guess I should contact my utility company!
One last point regarding my fellow tennants, the bulbs in the hallway are constantly burning out. I have not explicitly raised this issue with any of the neighbours but I will bring it up in our next condo meeting. I am quite sure that this is shared problem.
Thanks for the help it is greatly appreciated!