Speakerdude, I disagree; probably many insurance adjusters will also. It is not a good idea to run a 30-amp circuit regardless of any potential sonic improvements. It goes against electrical codes and for good reason. The limiting factor here is the rating of the receptacle - the 20A straight-blades (both slots up/down) cannot safely handle more than 20-amps continuous. If a fault occurs in the outlet box and the circuit starts drawing a continuous 27 or 28 amps, say, the required 20-A circuit breaker will clear the fault by tripping. An electrician can then determine what happened. If you have the 30-A breaker, it will happily let the excess current through and the mounting strap on the 20-A outlet, the plug and cord will heat up and possibly fail. This is a fire in the making.
The purpose of a circuit breaker is to protect the wire, period. It will not protect the outlet or your equipment. If all of your equipment draw more than 16-amps combined, then they need to be on multiple circuits because you will keep tripping the breaker. If one piece of equipment draws more than 20-amps, then something's wrong because the plug, cord and the transformer primary fuses are rated for a 20-amp (max) circuit. Hence the UL rating.
So if you go for #10 or #8 wiring (or even 500MCM for that matter) there might be benefits based upon your situation. However, your equipment will still draw only what's needed regardless of how much extra fat you have on the wires. But the circuit breaker has to prevent excess current from shooting through via faults or shorts. It's a safety thing, that's all.
The purpose of a circuit breaker is to protect the wire, period. It will not protect the outlet or your equipment. If all of your equipment draw more than 16-amps combined, then they need to be on multiple circuits because you will keep tripping the breaker. If one piece of equipment draws more than 20-amps, then something's wrong because the plug, cord and the transformer primary fuses are rated for a 20-amp (max) circuit. Hence the UL rating.
So if you go for #10 or #8 wiring (or even 500MCM for that matter) there might be benefits based upon your situation. However, your equipment will still draw only what's needed regardless of how much extra fat you have on the wires. But the circuit breaker has to prevent excess current from shooting through via faults or shorts. It's a safety thing, that's all.