Albert,
There's no way to separate a 2-pole 220v breaker to one side or the other. I think we all know that? No matter what you do the noise from your 220 circuits will always be present on either side of the panel.
You could in theory separate all your 110v breakers to one leg of the panel, but that's not necessarily a great idea.
The main objective when terminating a panel is "load balancing" That is to say an equal amount of amps on each side. This will reduce the load on the neutral conductor. When you have 50amps on one leg and 50 amps on the other there is zero amps on the neutral.
However if you had 100 amps on one leg and 10 amps on the other you would have 90 amps on the neutral (Grounded conductor) This poses some serious concerns. Electricians and engineers always seek to reduce the load on the neutral by distributing the load equally to both sides of a panel. The same holds true in three-phase power distribution.
You may also want to consider labeling your outlets with a P-touch labeler. You could mark the phase (A, B or C) plus the circuit number and panel designation. That may come in handy when moving things around.
Take care
Balancing the panel= Best installation
There's no way to separate a 2-pole 220v breaker to one side or the other. I think we all know that? No matter what you do the noise from your 220 circuits will always be present on either side of the panel.
You could in theory separate all your 110v breakers to one leg of the panel, but that's not necessarily a great idea.
The main objective when terminating a panel is "load balancing" That is to say an equal amount of amps on each side. This will reduce the load on the neutral conductor. When you have 50amps on one leg and 50 amps on the other there is zero amps on the neutral.
However if you had 100 amps on one leg and 10 amps on the other you would have 90 amps on the neutral (Grounded conductor) This poses some serious concerns. Electricians and engineers always seek to reduce the load on the neutral by distributing the load equally to both sides of a panel. The same holds true in three-phase power distribution.
You may also want to consider labeling your outlets with a P-touch labeler. You could mark the phase (A, B or C) plus the circuit number and panel designation. That may come in handy when moving things around.
Take care
Balancing the panel= Best installation