Help on basic 200 amp electrical service?


Here is an simple question. How can you tell if my house has 100 amp or 200 amp service? If I have 100 amp service what typically needs to be done to upgrade?

Thanks for the help and patience for my in learning in advance,
Al
dra1
Jeffcott,

Thanks for the perfectly worded answer. I added up everything in the house and if every thing is turned on from the stereo, oven, 2 A/C's, Well, clothes dryer, microwave, etc... to the last blow dryer and asuming everything runs all day long (which of course it doesn't), we are well away from 200 amps. I saved both your post and the Alaskan usage table.

My only goal which I should have said before after the saftey of the family was to see if my power senstive stereo was being fed enough. Since I am now comfortable with both, I rest easier and with my pocket a drop fuller not having to spend money and time on a electrician.

I am in your debt and greatly appreciate your time.

Thanks,
Al
If you want to know just the size of the service, the only two ways to do it is either to look in the service panel and see what the placard says, eg, "120/240 VAC 100-ampere" will tell you the maximum capacity of the panel is 100-amps. It doesn't matter what size the main fuse or circuit breaker is - as long as it's less than the panel rating.

If there is no placard, then the only other way to determine the size of the service is to ask an electrician what size is the meter pan or what size are the service wires coming in to the panel. (There's an easy way to determine this, but since you don't know about it, I'm certainly not going to send you fishing through your electric panel and hoping you don't get fried.)

All that said, there are basically three service sizes: 60-amp, 100-amp and 225-amp. Most houses with circuit breakers that have gas heat and cooking are 100-amp (or 60-amp if they have fuse boxes). Houses with electric stoves, electric heat, or well pumps will usually have 200/225 amp service. You can use your house as a guide.

Doing the math may tell you what you are using and give you an idea of what the minimum service size should be, but you cannot tell from this method because some people intentionally oversize the electrical service.
Dra1:
Gs5556 is absolutely correct. I read your inquiry incorrectly, now that I read it again. Gs is very knowledgeable and his response is exactly correct for your real question.