I only see one wire going to it and that wire goes to the inside of the meter housing.Foster_9,
That sounds like the remote read wiring for the water meter itself, has nothing to do with the grounding of the electrical service neutral conductor connection to earth.
In 1965 for the state and city you live in the AHJ, (authority having jurisdiction), the governing body electrical inspection department and probably the utility power company dictated the requirements for the grounding electrode, earth connection. NEC Code is only bare minimum electrical safety standards. I do know even back in 1965 the electrical service should have been grounded, connected to an approved grounding electrode per AHJ and or the utility power company.
From your original post,
Rereading the above comments you did not say the electrician actually said the incoming domestic water pipe was used as the grounding electrode, earth connection. He only said it would be safe it was used as the earth connection, the grounding electrode. Do you know for sure if the incoming domestic water line, pipe, is metallic, example copper, water piping at least 10' long buried in the earth outside your house?
When he checked out the panel, he noticed there is no earth ground to the panel. There is a ground wire going to the main water pipe, however. The electrician told me that the system is electrically safe with a ground only to the water pipe,
You do need to hire an electrician from your area. He will know what the local code for your area requires for the earth connection of the electrical service. You need to find out 100% whether the electrical service is earth grounded or not. If not get it done as soon as possible.
You also should think about replacing the Pushmatic electrical panel.
Just curious, the electrician that inspected the electrical service that told you it was not grounded, connected to earth, did he tell you then what would be required for him to ground the electrical service to meet electrical code for your area?
.