Jim, you do not understand, Krell runs 30 amp braker on every krell 700cx, 750mcx amp there at the factory, BTW, I have 4 fuses, well with-in the current capability useing a 30 amp breaker, as I said befor, I am not useing all the 30 amps!,however, This amp in particular spikes well above 20 amps while in use, maybe you should call krell, then you will get all the theory as to why this works properly you want, remeber, this amp at full power is 6,000 watts!
Audiolabyrinth,
IF, Krell is indeed telling customers the amp was designed to be connected to a 120V 30 amp branch circuit for use in the USA or Canada. Again IF!!!
You are the one that that does not understand what Krell is actually up to. If Krell is having to connect the amp to a 120V 30 amp circuit for the amp to operate properly as designed as well as to achive the amps reported specs then Krell should be using a captive power cord and a NEMA 125V 30 amp plug on the end of the cord. The user, customer, would then be required, per NEC Code, to install a 120V 30 amp branch circuit with the correct NEMA 125V 30 amp receptacle for the Krell amp plug. Per NEC Code a 30 amp branch circuit requires #10AWG minimum wire and shall be connected to a 30 amp branch circuit breaker, period. The receptacle must be a NEMA rated 125V 30 amp receptacle, period. No exceptions.
Instead Krell is apparently more interested in building a product that violates NEC code safety standards for the USA by using a 20 amp max rated IEC inlet connector on the amp where by the user can use a power cord that has a NEMA 5-15P or a NEMA 5-20P plug. Then Krell has the gull to tell a customer that bought the amp to change out the breaker at the electrical panel from a 20 amp to a 30 amp, which I believe the real reason is, because the Krell amp is nuisance tripping the 20 amp breaker on startup in rush current.
So because Krell was too tight to design/incorporate a soft start circuit to limit inrush current to solve the customer's problem of the 20 amp breaker nuisance tripping they tell the customer to change out the 20 amp breaker to a 30 amp breaker. What they should be telling the customer is to change out the 20 amp breaker to a 20 amp HM, High Magnetic, breaker that has a longer delay time for startup inrush current. Problem solved.
I wonder how many Krell users have followed the advice of krell? How many users who changed out the 20 amp breaker to a 30 amp on a 20 amp dedicated branch circuit that has #12AWG 20 amp rated wire?
As I have pointed out earlier in this thread the current carrying contacts as well as the other current carrying metal parts of a 20 amp breaker are identical to that of a 30 amp breaker. Had an EE at Krell done his/her homework he/she would know this as well. They would also know as well a typical TM, thermal magnetic, breaker will easily pass short bursts of current of 120 amps all day long. More than enough for their amp but not enough apparently for startup inrush current. A 30 amp TM breaker will pass short bursts of 300 amps. Hell you can arc weld with 120V at 30 amps. And if the branch circuit wire is of any length and #12AWG copper once I get the #12 branch circuit wire cooking I won't have to worry about tripping the 30 amp breaker.
I have looked at every article in NEC Code that pertains to the code violations and nowhere in the NEC Code book is an exception given for Krell inc.
Audiolabyrinth , did you know?
NEWS from CPSC
U.S. Consumer Product Safety Commission
Office of Information and Public Affairs Washington, DC 20207
August 19, 2009
Release # 09-312
Firm's Recall Hotline: (888) 436-6055
CPSC Recall Hotline: (800) 638-2772
CPSC Media Contact: (301) 504-7908
Amplifiers Recalled by Krell Industries Recalled Due to Fire Hazard
WASHINGTON, D.C. - The U.S. Consumer Product Safety Commission, in cooperation with the firm named below, today announced a voluntary recall of the following consumer product. Consumers should stop using recalled products immediately unless otherwise instructed. Units:
Distributor: Krell Industries LLC, of Orange, Conn.
Hazard: The amplifiers were designed to operate at a temperature warm to the touch. However, a component input device can fail and cause the amplifiers to overheat, posing burn and fire hazards to consumers.
Incidents/Injuries: Krell has received 50 reports of the amplifiers overheating including reports of smoke and electrical fire. No injuries have been reported.
Description: This recall involves Krell power amplifiers with model numbers KAV-250a, KAV-250a/3, KAV-500i and KAV-1500. The amplifiers are used to provide power to a loudspeaker in a home audio playback system. The Krell logo is printed on the front of the amplifier.
Sold by: Authorized dealers and distributors of audio equipment nationwide from January 1997 through February 2001 for between $3,000 and $8,000.
Manufactured in: USA
Remedy: Consumers should immediately stop using the amplifiers, and contact Krell to schedule the free installation of replacement fuses.
Consumer Contact: For additional information contact Krell at (888) 436-6055 between 9 a.m. and 4:30 p.m. ET Monday through Friday, or visit the firm's Web site at www.krellonline.com. Consumers can also email the firm at service@krellonline.com
Krell recallI would bet that no owner of the Krell amp mentioned in this thread has anything in writing from a representative of Krell inc. stating Krell recommends changing the breaker on a 20 amp branch circuit from a 20 amp to a 30 amp breaker. All a user/customer has is a verbal conversation that is worthless in a court of law.
So who is in violation of State, and local governing body safety electrical codes and electrical safety standards when a 20 amp breaker is changed out to a 30 amp breaker on a 20 amp branch circuit?
. The person/home owner that changes it out of course.
I suggest you call you insurance agent and ask him/her if you are covered by your home owners insurance policy in the event of an electrical fire if it is found a 30 amp breaker is installed on a 20 amp branch circuit.
Then call the governing electrical inspection department in your city and ask them about changing the 20 amp breaker to a 30 amp breaker on a 20 amp branch circuit.
NEC Code
210.21 (B)(3) Receptacle Rating.
Where connected to a branch circuit supplying two or more receptacles or outlets, receptacles ratings shall conform to the values listed in table 210.21(B)(3), ...........
NEC Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits.
Circuit Rating ..... Receptacle Rating
(Amperes) .............. (Amperes)
15 ............................ 15
20 ....................... 15 or 20
30 ............................ 30
Minimum wire size #10awg. Breaker size 30 amp.
*No exception given for Krell Inc.
Circuit Breaker MythsSiemens BreakersElectrical-forensics.