"But installing such a breaker without upgrading the associated wiring would be foolhardy and would not meet code in any state in the country."
Well said.
Well said.
Amp and preamp on same outlet?
Audiolabyrinth, IF, Krell is indeed telling customers the amp was designed to be connected to a 120V 30 amp branch circuit for use in the USA or Canada. Again IF!!! You are the one that that does not understand what Krell is actually up to. If Krell is having to connect the amp to a 120V 30 amp circuit for the amp to operate properly as designed as well as to achive the amps reported specs then Krell should be using a captive power cord and a NEMA 125V 30 amp plug on the end of the cord. The user, customer, would then be required, per NEC Code, to install a 120V 30 amp branch circuit with the correct NEMA 125V 30 amp receptacle for the Krell amp plug. Per NEC Code a 30 amp branch circuit requires #10AWG minimum wire and shall be connected to a 30 amp branch circuit breaker, period. The receptacle must be a NEMA rated 125V 30 amp receptacle, period. No exceptions. Instead Krell is apparently more interested in building a product that violates NEC code safety standards for the USA by using a 20 amp max rated IEC inlet connector on the amp where by the user can use a power cord that has a NEMA 5-15P or a NEMA 5-20P plug. Then Krell has the gull to tell a customer that bought the amp to change out the breaker at the electrical panel from a 20 amp to a 30 amp, which I believe the real reason is, because the Krell amp is nuisance tripping the 20 amp breaker on startup in rush current. So because Krell was too tight to design/incorporate a soft start circuit to limit inrush current to solve the customer's problem of the 20 amp breaker nuisance tripping they tell the customer to change out the 20 amp breaker to a 30 amp breaker. What they should be telling the customer is to change out the 20 amp breaker to a 20 amp HM, High Magnetic, breaker that has a longer delay time for startup inrush current. Problem solved. I wonder how many Krell users have followed the advice of krell? How many users who changed out the 20 amp breaker to a 30 amp on a 20 amp dedicated branch circuit that has #12AWG 20 amp rated wire? As I have pointed out earlier in this thread the current carrying contacts as well as the other current carrying metal parts of a 20 amp breaker are identical to that of a 30 amp breaker. Had an EE at Krell done his/her homework he/she would know this as well. They would also know as well a typical TM, thermal magnetic, breaker will easily pass short bursts of current of 120 amps all day long. More than enough for their amp but not enough apparently for startup inrush current. A 30 amp TM breaker will pass short bursts of 300 amps. Hell you can arc weld with 120V at 30 amps. And if the branch circuit wire is of any length and #12AWG copper once I get the #12 branch circuit wire cooking I won't have to worry about tripping the 30 amp breaker. I have looked at every article in NEC Code that pertains to the code violations and nowhere in the NEC Code book is an exception given for Krell inc. Audiolabyrinth , did you know? Krell recall I would bet that no owner of the Krell amp mentioned in this thread has anything in writing from a representative of Krell inc. stating Krell recommends changing the breaker on a 20 amp branch circuit from a 20 amp to a 30 amp breaker. All a user/customer has is a verbal conversation that is worthless in a court of law. So who is in violation of State, and local governing body safety electrical codes and electrical safety standards when a 20 amp breaker is changed out to a 30 amp breaker on a 20 amp branch circuit? . The person/home owner that changes it out of course. I suggest you call you insurance agent and ask him/her if you are covered by your home owners insurance policy in the event of an electrical fire if it is found a 30 amp breaker is installed on a 20 amp branch circuit. Then call the governing electrical inspection department in your city and ask them about changing the 20 amp breaker to a 30 amp breaker on a 20 amp branch circuit. NEC Code 210.21 (B)(3) Receptacle Rating. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacles ratings shall conform to the values listed in table 210.21(B)(3), ........... NEC Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits. Circuit Rating ..... Receptacle Rating (Amperes) .............. (Amperes) 15 ............................ 15 20 ....................... 15 or 20 30 ............................ 30 Minimum wire size #10awg. Breaker size 30 amp. *No exception given for Krell Inc. Circuit Breaker Myths Siemens Breakers Electrical-forensics . |
See page #5 Full Power Balanced X Series Power Amplifiers
Note the word [minimum] used for the "750Mcx, 400cx, and 450Mcx amplifiers need to be operated from a dedicated AC power line rated at a minimum of 20 amps." If the equipment is manufactured for use in the USA with the intent of using a power cord with a NEMA 5-20P 125V 20 amp plug then the max branch circuit ampacity rating is 20 amps. Period! The minimum branch circuit ampacity rating because of the NEMA 5-20P plug is 20 amps. Period! Minimum wire size #12AWG copper. Branch circuit breaker size, 20 amp. Period! Receptacle, if the Krell power cord plug is a NEMA 5-20P plug then a NEMA 5-20R 125V 20 amp receptacle for the plug to fit it is required. All the above are NEC Code minimum electrical safety standard requirements. Krell can spec #10 AWG copper wire, which I would recommend. For long branch circuit runs maybe even #8 AWG Cu. They can spec an HM, High Magnetic, 20 amp breaker must be used to help prevent nuisance breaker tripping. They should spec that only power cords that has a NEMA 5-20P plug can be used with a minimum cord conductor wire size of #10AWG. They can spec only a NEMA 5-20R 125V 20 amp heavy duty commercial/industrial rated receptacle be used. The bigger wire and heavy duty receptacle will help reduce voltage sag on the branch circuit wiring, receptacle contacts to plug blades, and power cord wire right up to that 20 amp IEC inlet connector mounted on the back of the unit caused by the Krell amp's dynamic power connected load. They cannot spec a 30 amp circuit breaker be used on a 20 amp branch though. You will notice in the owner manual a 30 amp branch circuit was not mentioned. Everybody reading this thread by now should know the reason why. . |
Edit for previous first post dated 03-03-15: Jea48 NEC Code 210.21 (B)(3) Receptacle Rating. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacles ratings shall conform to the values listed in table 210.21(B)(3), ........... NEC Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits. Circuit Rating ..... Receptacle Rating (Amperes) .............. (Amperes) 15 ............................ 15 20 ....................... 15 or 20 30 ............................ 30 Minimum wire size #10awg. Breaker size 30 amp. *No exception given for Krell Inc. >>>>>>>>>>>>>>>>>>>>>>> Strike, Minimum wire size #10awg. Breaker size 30 amp. and replace with, The branch circuit breaker size determines the size of the branch circuit. If the branch circuit breaker is 30 amp then the minimum wire size must be #10 AWG. It can be bigger but it cannot not smaller. The receptacle must be a NEMA 125V 30 amp rated receptacle. It cannot be bigger, it cannot be smaller, it can only be a NEMA 30 amp rated receptacle. . |