See page #5
Full Power Balanced
X Series Power Amplifiers
Note the word [minimum] used for the "750Mcx, 400cx, and 450Mcx amplifiers need to be operated from a dedicated AC power line rated at a minimum of 20 amps."
If the equipment is manufactured for use in the USA with the intent of using a power cord with a NEMA 5-20P 125V 20 amp plug then the max branch circuit ampacity rating is 20 amps. Period! The minimum branch circuit ampacity rating because of the NEMA 5-20P plug is 20 amps. Period!
Minimum wire size #12AWG copper.
Branch circuit breaker size, 20 amp. Period!
Receptacle, if the Krell power cord plug is a NEMA 5-20P plug then a NEMA 5-20R 125V 20 amp receptacle for the plug to fit it is required.
All the above are NEC Code minimum electrical safety standard requirements.
Krell can spec #10 AWG copper wire, which I would recommend. For long branch circuit runs maybe even #8 AWG Cu.
They can spec an HM, High Magnetic, 20 amp breaker must be used to help prevent nuisance breaker tripping.
They should spec that only power cords that has a NEMA 5-20P plug can be used with a minimum cord conductor wire size of #10AWG.
They can spec only a NEMA 5-20R 125V 20 amp heavy duty commercial/industrial rated receptacle be used.
The bigger wire and heavy duty receptacle will help reduce voltage sag on the branch circuit wiring, receptacle contacts to plug blades, and power cord wire right up to that 20 amp IEC inlet connector mounted on the back of the unit caused by the Krell amp's dynamic power connected load.
They cannot spec a 30 amp circuit breaker be used on a 20 amp branch though. You will notice in the owner manual a 30 amp branch circuit was not mentioned. Everybody reading this thread by now should know the reason why.
.
Full Power Balanced
X Series Power Amplifiers
AC POWER GUIDELINES
The Full Power Balanced 300cx and 350Mcx
amplifiers need to be operated from a dedicated
AC power line rated at a minimum of 15
amps. The Full Power Balanced 700cx,
750Mcx, 400cx, and 450Mcx amplifiers need to
be operated from a dedicated AC power line
rated at a minimum of 20 amps.
Please contact your authorized Krell dealer, distributor,
or Krell before using any devices
designed to alter or stabilize the AC power for
Full Power Balanced amplifiers.
Note the word [minimum] used for the "750Mcx, 400cx, and 450Mcx amplifiers need to be operated from a dedicated AC power line rated at a minimum of 20 amps."
If the equipment is manufactured for use in the USA with the intent of using a power cord with a NEMA 5-20P 125V 20 amp plug then the max branch circuit ampacity rating is 20 amps. Period! The minimum branch circuit ampacity rating because of the NEMA 5-20P plug is 20 amps. Period!
Minimum wire size #12AWG copper.
Branch circuit breaker size, 20 amp. Period!
Receptacle, if the Krell power cord plug is a NEMA 5-20P plug then a NEMA 5-20R 125V 20 amp receptacle for the plug to fit it is required.
All the above are NEC Code minimum electrical safety standard requirements.
Krell can spec #10 AWG copper wire, which I would recommend. For long branch circuit runs maybe even #8 AWG Cu.
They can spec an HM, High Magnetic, 20 amp breaker must be used to help prevent nuisance breaker tripping.
They should spec that only power cords that has a NEMA 5-20P plug can be used with a minimum cord conductor wire size of #10AWG.
They can spec only a NEMA 5-20R 125V 20 amp heavy duty commercial/industrial rated receptacle be used.
The bigger wire and heavy duty receptacle will help reduce voltage sag on the branch circuit wiring, receptacle contacts to plug blades, and power cord wire right up to that 20 amp IEC inlet connector mounted on the back of the unit caused by the Krell amp's dynamic power connected load.
They cannot spec a 30 amp circuit breaker be used on a 20 amp branch though. You will notice in the owner manual a 30 amp branch circuit was not mentioned. Everybody reading this thread by now should know the reason why.
.