Yes, both ground wires from the outlet/metal box are attached to the ground bar in the sub panel.
Glad to hear that. That’s the way it should be done.
You would be surprised how many posted messages I have read over the years on audio forums where the IG safety equipment grounding conductor was connected directly to the earth connection (Grounding Electrode) for the main electrical service. Or the IG ground was connected to an isolated earth driven ground rod that is not tied, bonded, to the main grounding system of the electrical service, which is quite dangerous. Neither of the two methods meet NEC code.
The purpose of the equipment grounding conductor is to provide a low resistive path for ground fault current to return to the source, the electrical service grounded neutral conductor.
The 2 ought from the sub panel runs back to the main panel. The main panel is grounded to the steel rebar in the house foundation
Just curious, did the electrician wire the new sub panel 120/240V?
2 hot wires, 1 neutral wire, and 1 equipment ground wire.
Did he use 1/0 - 3 with ground romex?
Metal conduit and install three 1/0 conductors plus an insulated equipment ground conductor?
1/0 - 3 with ground MC (Metal Clad) armor cable?
How far (distance) is the sub panel from the main electrical service panel?
If the sub panel is 120/240V did you tell the electrician to feed all 6 dedicated 120V branch circuits from the same Line, leg, from the panel? All from Line 1 (L1) or all from Line 2 (L2)? Audio equipment that is connected together by wire ICs should be fed from circuit breakers fed from the same hot Line, leg, and neutral.
What manufacture brand electrical panel did he install? Style/model? Copper bus? Example, Square D QO.
.
What is the average length of the 6 dedicated 20 amp branch circuits? Longest? Shortest?
How did the electrician terminate, connect, the #6 wire to the 20 amp circuit breakers?
//
Are the six 20 amp circuit breakers CAFCI ( Combination Arc Fault Circuit Interrupter) type?
Example: http://www.homedepot.com/p/Square-D-QO-20-Amp-Single-Pole-CAFCI-Circuit-Breaker-QO120CAFIC/202353307...
Or maybe this style, a plug on neutral CAFI breaker/panel system.
http://www.schneider-electric.us/en/product-range/62194-qo-plug-on-neutral-cafi-circuit-breakers/
How did the electrician terminate the #6 neutral wire to the breaker?
IF the sub panel is a Load Center panel it must look pretty busy, full, inside. (A Load Center electrical panel is the type of panel used typically in a residential dwelling unit.)
Or did the electrician install an actual electrical panelboard that is physically much bigger than a Load Center. Lots more wiring space inside. About twice the price of a Load Center.
.