I am told to plug the power amp straight to the outlet rather than the power conditioner. Since I am remodeling my home so I am going to have electrician to install the outlet, one outlet per amp and each outlet has individual circuit breaker. Then he asks me if I want 20amp or 30amp since I told him high current.
what do I need? 20amp or 30amp circuit breaker? Thanks.
what do I need? 20amp or 30amp circuit breaker? Thanks.
- ...
- 33 posts total
hifiman5 Dude...read what the quote above says...its a DRYER power receptacle. All you do is hook up 10 gauge wire to a 30 amp breaker to a regular power outlet and you are good to goWhat I showed you is a 30A outlet, which is commonly used for dryers, "dude." Putting a 30A breaker on a 30A line - but connected to a 20A receptacle, is a code violation, for the reasons I previously stated. It's a fire hazard. |
hifiman5 @cleeds I guess the electrician who willingly installed that line in that outlet was violating code? The building inspector too? HmmmCodes vary by location; the NEC establishes only the minimum guidelines. If your inspector approved the install and you're comfortable with that, that's fine. If you don't see the possible hazard of putting a device rated at only 20A on a line capable of delivering 30A through it, then there's nothing further I can add. It's surely a risk I wouldn't and didn't take. Instead, I built several 30A lines, but used a 20A breaker on each. That's a common and perfectly acceptable practice. |