Go for the 10-3. 20 amps is more than enough. 15 amps is as well. 2 15 amp circuits is 30 X 120 = 3,600 Watts. With a 20 foot run, the costly, cryo-treated, blah blah blah cable is simply bragging rights. It's your money. But get good quality breakers. ABB is the preferred brand. The Oxide outlets are very good. If you want the pretty carbon fiber, super duper covers - again, your money. Metal, brass or stainless steel works as good if not better. Carbon fiber is resistive and won't shunt any applied energy (interference) as well.
Romex and breaker switches
I did a search and have read previous posts, but I still have some questions. I had an electrician install dedicated lines in my listening room when we built our house 20 years ago. I bought simple hospital grade outlets from a big box store and did not specify the gauge of the romex or anything else. I need to clear out my dedicated listening room soon for new hardwood to be installed and figured now would be a good time to revisit and improve my dedicated lines. I have already bought a pair of Oyaide R1 duplexes and intend to have them installed side by side behind my equipment rack. My question is-is there a particular variation of 10 gauge romex that would be best? I have looked and there are quite a few variations including 10-2 and 10-3 and I have no idea what to buy or for that matter, if some other wire that would do the job and not be prohibitively expensive presents a better option. I will need a 20 foot run for each duplex. Also, can someone help me as to whether the breaker switch on my panel matters much and whether I should opt for 20A, 30A, or other? I now know that all runs from my duplexes to the panel should be to the same leg. I will make sure that happens. Any other recommendations or advice about romex/wire to use and breaker switches given my decision to go with Oyaide R1's would be most appreciated.
- ...
- 43 posts total
"There can be advantages to using 10 gauge wire on a 20A circuit, including reducing voltage drop. It is difficult to work with, and using a pigtail into the outlet does make it easier to terminate." Not only is this a Code Violation, this is a MAJOR fire hazard. Tha ampacity of the wire cannot exceed the ampacity of the breaker. If running multiple circuits, separate neutrals (although not necessary} is a good idea. Jeff {retired electrician Local 41 IBEW} |
I'm with Jeff. Run two 20 amp 12-2 lines directly from the breaker panel. Use whatever breakers your box takes Murray for Murray, etc. Dedicate one circuit to the power amp. No pig tailing bigger wire to smaller. No using a 30 amp breaker - you want it to trip if there's a problem! I heard BX painted metal flake electric blue sounds best. As long as the flakes in the paint are aligned by an electrostatic cyrocoating process. |
audioslain02 "There can be advantages to using 10 gauge wire on a 20A circuit, including reducing voltage drop. It is difficult to work with, and using a pigtail into the outlet does make it easier to terminate."You misread what I wrote. It is certainly within code to use 10 ga. wire on a 20A circuit, which requires by definition a 20A breaker. There are large potential advantages to doing just that, and it has worked very well in my system. It is actually a fairly common practice and exceeds the NEC, which only sets minimum standards. |