erik_squires Add more ground rods.
Bond them to house ground rod farm. Run 1 ground wire directly to the ground rods, and use that for your outlets.
Not sure what you are recommending to the OP. Would you please expand.
NEC requires the equipment grounding conductor to be installed in the same raceway or part of the same cable assembly, (Example Romex).
NEC does allow an Auxiliary Grounding Electrode. NEC 250.54... I wouldn’t recommend it. It supplies a path for lightning to enter the OPs home.
2008 NEC—250.54
Auxiliary Grounding Electrodes.
One or more grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as an effective ground-fault current path as specified in 250.4(A)(5) and 250.4(B)(4).
https://www.ecmag.com/section/codes-standards/significant-changes-nec-2008-0The Aux grounding Electrode Shall connect to the branch circuit equipment grounding conductor. Lightning loves an Aux grounding electrode.
.