Your branch circuit wiring is more than likely installed in EMT (Electrical Metallic Tubing).
https://www.homedepot.com/p/1-2-in-x-10-ft-Electric-Metallic-Tube-EMT-Conduit-853428/100400405
Per the NEC the EMT conduit is considered an equipment grounding conductor, Not sure if Chicago AHJ does though. I would imagine they do. Therefore per NEC the steel outlet box and supporting back strap of the IG duplex receptacle is grounded.
Stop!
Find another electrician! Keep looking.
This guy sits on one of the NEC (National Electrical Code) boards that helps write electrical safety code.
Watch the video.
https://www.youtube.com/watch?time_continue=2&v=qNZC782SzAQ
Now what did the electrician tell you over the phone again?
I know Chicago has good electricians.
Jim
.
Your branch circuit wiring is more than likely installed in EMT (Electrical Metallic Tubing).
https://www.homedepot.com/p/1-2-in-x-10-ft-Electric-Metallic-Tube-EMT-Conduit-853428/100400405
Per the NEC the EMT conduit is considered an equipment grounding conductor, Not sure if Chicago AHJ does though. I would imagine they do. Therefore per NEC the steel outlet box and supporting back strap of the IG duplex receptacle is grounded.
Now I talked to another electrician just now and he said to me that the way green wire is done it is probably not up to code but he said that even they (then) it is should not be a problem.
Stop!
Find another electrician! Keep looking.
This guy sits on one of the NEC (National Electrical Code) boards that helps write electrical safety code.