How to remove ground pin on power cable


This is a power cable being used for my subwoofer. I have a ground loop currently. According to the manufacturer of my subwoofer, due to it's design, it is perfectly safe to remove the ground. Right now I do so with a cheater plug but I would like to avoid having to use it. The power cable in question is Oyaide Black Mamba V2

How easy is it to take a power cable apart and disconnect the ground? Is it best to do so at the IEC side or the pronged side? What is the process for doing this?

Thanks
nemesis1218
Post removed 
So you guys think its fair to nitpick me to death, then remove my post so people don’t get the explanation. Its okay for you to use my words, but not me. Someone, not all but some number of you, are the most despicable spineless weasely lowlifes imaginable. 
millercarbon
So you guys think its fair to nitpick me to death, then remove my post so people don’t get the explanation.
No one here has nitpicked - they've corrected your profound errors, that you then punctuate with proclamations such as:
That's how I defend my position. By being right. Works every time.
It seems to me that others here have been more respectful of you that you have of them.

Your post could only have been removed by moderators so if you're unhappy that it was deleted, your ire should be directed to them.
The reason, as I recall, for neutral and ground being separated has to do with Ohms law.

Neutral is a working conductor in the sense that it SHOULD normally carry 100% of the current the hot does. So, 15-20 amps in a typical residential application.

Due to many factors, the impedance of neutral can become significantly non-zero.

15 A * 0 Ohms = 0V

15 A * 5 Ohm = 75 V

etc. etc.

So it is quite possible, if not probable that neutral can be non zero. Now imagine if that the ground wire no longer exists (as in old homes/appliances), but the chassis of your equipment is bonded to neutral (old washer/dryers). See the problem? You now have gear which can develop a significant shock factor by touching it. Happened to me with an
old dryer once. :)

The entire point of a safety ground in appliances is to have any voltage which accidentally touches the chassis to drain to ground and hopefully blow a fuse or breaker.

Of course, faults can happen in the ground conductor as well, but operationally, if the ground develops a high impedance, it’s not going to normally develop a voltage because current = 0.

This part is kind of important:

Because each panel can introduce a new impedance problem, the neutral and ground must remain unbonded except at the service panel. The service panel is the first one after the meter. So, if you add subpanels, you run 4 conductors. +120, -120, Neutral and Ground. One trick here is that the ground may form a loop. You don’t necessarily have to pull the ground from the panel....but that leaves open the possibility of a future contractor not knowing this, so don’t.

This concludes my Ted talk.