If you install a 20-amp breaker, run a #12 or #10 branch circuit and install a Nema 5-20R receptacle, that will cover all 120 volt options for 15 or 20 amps.
My advice: use romex 10/3. Cut the bare ground and use the insulated red for ground connected to the receptacle ground screw. Be sure to put green tape on the red wire where it is visible. This feeder works the best IMO since all the wires are twisted at the factory. The twist helps cancel common mode noise. The worst wire to use is 2-wire romex because the hot and neutral are parallel to each other, which makes it a very efficient RF antenna.
My advice: use romex 10/3. Cut the bare ground and use the insulated red for ground connected to the receptacle ground screw. Be sure to put green tape on the red wire where it is visible. This feeder works the best IMO since all the wires are twisted at the factory. The twist helps cancel common mode noise. The worst wire to use is 2-wire romex because the hot and neutral are parallel to each other, which makes it a very efficient RF antenna.