When A Lightening Strike Blows Your Power Company’s Transformer Off Its Utility Pole ………


A good friend of mine with about $20,000 invested in his audio system recently emailed me asking for my thoughts on what he should upgrade next. He said his budget was about $2,000, and he said he was considering a major upgrade to his Linn analog setup. He knows I love vinyl as I have a fully tricked out Michell GyroDec with their first external outboard power supply (The original was AC powered but because a supplier discontinued a vital part they had to re-engineer it as a DC power supply. I thought about what I would recommend to my friend. While thinking, I reflected on my own journey through this wonderful hobby we share, and then I remembered a potentially disastrous event that affected us when my wife and I lived in central Texas. And I was grateful that we dodged a huge bullet at the time. So I wrote him back and said:

If it were me, I’d spend the money on a good electrician: First, I’d have him install and properly ground a whole house surge protector. They can actually save your system and everything electrical in your home. A few years back I lived in Arlington, TX. We had a bad thunderstorm roll through one afternoon and lightning struck the transformer that fed our home and several others, and it blew the transformer off the pole into my backyard. I incurred ZERO damage, and my power feed was the closest to the transformer.

My neighbor on our left lost EVERYTHING that was plugged into an outlet, including their stove, refrigerator, D/W, water heater, and their HVAC. Even worse, all of their home’s interior electrical wiring was fried and the entire house had to be re-wired. Their insurance company was only willing to replace everything with all inside wiring in code-approved conduit and conduit mounted outlets that would be placed on the bottom outside of their walls in all the interior rooms (they would have been ugly as hell).

The neighbor paid extra to have electricians fish new wiring from the attic so the wiring would be like (and look like) it was before the strike. This was an expensive extra cost NOT COVERED by their H/O policy. It was August in central Texas and an electrician could only last about 60 minutes in the attic as the attic temperature ranged from 130F to 140F. And they had to shop for and purchase all new appliances, install a new HVAC, and live in a hotel room for two months while all this work was being done.

My neighbor on the other side had a few of the $20 - $30 plug-in surge protectors like they sell at Lowe’s and Home Depot, and they were all fried as was everything that was plugged into them that they were allegedly protecting. The stuff that was plugged into a 240V outlet mostly survived, but their stove lost its clock and timer settings, their refrigerator’s temperature settings could no longer be adjusted, and their dryer somewhat worked but you could not set the drying time or temperature. 
After the electrician got the surge protector installed a grounded, I would have them run at least two (three is better) 120V 20amp feeds directly to your listening room for your system. Make SURE to have the electrician run each new feed to a SEPARATE breaker in your electrical panel. Your system will sound better and thank you! 😃

All of this pain could likely been avoided by both neighbors if they had simply invested in a $150 -$250 whole house surge protector properly installed and properly grounded when they moved into their home. I’m retired now, but I previously worked in the corporate world and my wife and I relocated and purchased and lived in 8 different homes over the course of my 35 year career. 
The very first thing we would do after closing and moving into our new home would be to find a reputable licensed electrician and have them install and ground a whole-house surge protector. I would next have the electrician run at least two, sometimes three dedicated 120V 20 amp circuits to the room that was going to be our listening room in the area where I was going to install our audio system. And I made certain that each of these new lines were connected to their own breaker in the fuse panel and that nothing else was shared on this circuit.

Like I said earlier we incurred zero damage from this strike, and I immediately replaced my fried whole-house surge protector after this incident. As always, YMMV 😎
128x128vinyl_rules
I’m not sure about the value off a separate panel off the main supply as you still only have the single electrical line feeding your home.

Benefits:

  • Ease of running additional circuits
  • Reduction in voltage drop thanks to the massive cable you will run to your sub panel. If memory serves, you get better voltage this way than running individual lines all the way back.  It's been a while since I did the math though, others with more recent electrical experience should double check me.
  • The possibility of running 220V conditioners/transformers at the sub panel.

OP said:
A few years back I lived in Arlington, TX. We had a bad thunderstorm roll through one afternoon and lightning struck the transformer that fed our home and several others, and it blew the transformer off the pole into my backyard. I incurred ZERO damage, and my power feed was the closest to the transformer.
You were just lucky that day. The SPD (Surge Protection Device) did not save your home that day, jmho.

Just curious was the overhead power line from the transformer to the house broken, knocked to the ground, at the pole by the lightning strike physical damage to the pole and transformer? If yes that might explain why your house was spared.

Here is some SPD reading material.
https://www.nemasurge.org/faqs/

What are surges, transients, and temporary over-voltages, and what are their typical characteristics?

Although often used as separate terms in the surge industry, Transients and Surges are the same phenomenon. Transients and Surges can be current, voltage, or both and can have peak values in excess of 10kA or 10kV. They are typically of very short duration (usually >10 µs & <1 ms), with a waveform that has a very rapid rise to the peak and then falls off at a much slower rate. Transients and Surges can be caused by external sources such as lightning or a short circuit, or from internal sources such as Contactor switching, Variable Speed Drives, Capacitor switching, etc.

Temporary over voltages (TOVs) are oscillatory
phase-to-ground or phase-to-phase overvoltages that can last as little as a few seconds or as long as several minutes. Sources of TOV’s include fault reclosing, load switching, ground impedance shifts, single-phase faults and ferroresonance effects to name a few. Due to their potentially high voltage and long duration, TOV’s can be very detrimental to MOV-based SPD’s. An extended TOV can cause permanent damage to an SPD and render the unit inoperable. Note that while ANSI/UL 1449 ensures that the SPD will not create a safety hazard under these conditions; SPDs are typically not designed to protect downstream equipment from a TOV event.

TOP

What are multi-mode SPDs – why do I need L-L (line-to-line) and N-G (neutral-to-ground) protection?

Multi-mode surge protective devices (SPDs) are devices which comprise a number of SPD components within the one package. These “modes” of protection can be connected L-N, L-L, L-G and N-G across the three phases. Having protection in each mode provides the protection for the loads particularly against the internally generated transients where ground may not be the preferred return path. In some applications such as applying an SPD at a service entrance where both the neutral and ground points are bonded there is no benefit of seperarate L-N and L-G modes, however as you go further into the distribution and there is separation from that common N-G bond, the SPD N-G mode of protection will be beneficial.




Here is a video showing what happened when a power transformer failed.

https://www.wwltv.com/article/news/local/jefferson/transformer-blows-in-kenner-killing-power-for-mor...

An SPD would be worthless in this instance if the high voltage power came in on the electrical service wiring of a home.
It is really hard to say how much a surge protector system will protect  your home.   They help immensely, to be sure, but keep in mind the average lightening bolt has the equivalent energy to lift the RMS Titanic six miles off the ocean floor and set it on a barge 5 feet above the surface of the water.   The displacement of the RMS Titanic is 52,310 tons.   Yeah, there is some serious energy there.   You might be okay, you might not, but you are definitely better with a big professional system than without it, even if everything is fried.   I worked for a guy who had a lightening bolt hit his chimney.  It cracked the bricks and the resulting EMP pulse took out everything, regardless if it was on or not. 
Jea48 said:

”Just curious was the overhead power line from the transformer to the house broken, knocked to the ground, at the pole by the lightning strike physical damage to the pole and transformer? If yes that might explain why your house was spared.”

To the best of my recollection the power line to my home was still attached to wiring at the top of the utility pole. The transformer was laying on the concrete deck of my swimming pool with no lines attached to it.

And yes, I was VERY lucky that day. 😱

vinyl_rules OP  

02-23-2021  
 5:00pm


To the best of my recollection the power line to my home was still attached to wiring at the top of the utility pole. The transformer was laying on the concrete deck of my swimming pool with no lines attached to it.

And yes, I was VERY lucky that day. 😱

One other thing that may have been at play that day was the integrity, conductivity, of the electrical service of your home’s System Ground / Grounding Electrode System. The Grounding Electrode System is the grounding used to connect the electrical service entrance neutral conductor and service equipment ground to mother earth. The lower the impedance connection to earth the better the conductivity for diverting lightning and or a high voltage transmission line fault to mother earth.
IEEE recommends 5 ohms or less grounding electrode to soil resistance.

Here is some reading material.

https://www.ecmag.com/section/codes-standards/grounding-electrode-conductors-building

http://www.inspectionbureau.com/studyGuides/GroundingElectrodeSystems17.pdf

.