I think you've now protected your 12 wire circuits with a 40A breaker, which is a huge mistake.
That being said, wait for jea48 to answer.
That being said, wait for jea48 to answer.
Power conditioning for multiple dedicated circuits
Since this is a DOUBLE POLE 40 A breaker, each 12 gauge line gets it's own 20A breaker as you have already stated. Since this is a double pole breaker, that means that each 20 A side gets it's own phase as well. That is how your AC panel is set up. So far, I see this all to be an advantage, except for the shared ground and neutral. Not sure what limitations or problems that may cause, if any. |
I'm not suggesting power conditioners don't work- in fact, they may work effectively in eliminating more than what you intended.True Most of the ac mains "dirty power" found in our houses is caused by devices, equipment, and appliances, found in the home. Including the audio equipment itself. As for dirty power put back out on the ac mains by the audio equipment, that is why more than one dedicated branch circuit is used. YMMV. |
builder3454 postsCorrect. The breaker needs to be a 2 pole 20 amp breaker. |
dhite71 OP147 posts I did the 2nd scenario you described. I chose this because when I went to Lowes to pick up the Romex they had a bundle of 12/3 wire that was 1/2 price due to a return.It’s nuts what Romex is selling for now. You can buy 12/2 and 12/3 MC (Metal Clad) aluminum armor cable cheaper than Romex. Supply and demand! Before I explain where, imo, you went wrong in the type of wiring and wiring methods you used please explain why you are looking at buying plug in power conditioners? Are trying correct something? Are you hearing something from the speakers of your system you don’t like? Did you hear it before you added the 4 new circuits? . |