I would be remiss if I did not mention if an Electrical Contractor/Electrician was hired to install four 120V branch circuits he/she would not install MWBC (s). The reason is the NEC requires all new 15A and 20A branch circuits supplying outlets, per 210.12 (A), shall be AFCI protected. The problem with using a MWBC the 2 pole breaker will nuisance trip for no apparent reason because of the shared neutral.
Example of a 2 pole 15A or 20A AFCI breaker:
https://www.homedepot.com/p/Square-D-QO-20-Amp-2-Pole-Combination-Arc-Fault-Circuit-Breaker-QO220CAF...
NEC (National Electrical Code)
210.12 Arc-Fault Circuit Interrupter Protection.
Arc-fault circuit-interrupter protection shall be provided as required in 210.12 (A), (B), (C), and (D).
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6).
.
Example of a 2 pole 15A or 20A AFCI breaker:
https://www.homedepot.com/p/Square-D-QO-20-Amp-2-Pole-Combination-Arc-Fault-Circuit-Breaker-QO220CAF...
NEC (National Electrical Code)
210.12 Arc-Fault Circuit Interrupter Protection.
Arc-fault circuit-interrupter protection shall be provided as required in 210.12 (A), (B), (C), and (D).
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6).
.