@erik_squires Said:
If you have a different ground, it’s no longer the zero point, and when a short occurs you are no longer guaranteed it will be at 0.
In the event of a Hot 120V ground fault to an isolated dedicated ground rod the voltage WILL NEVER be zero. The Step Potential voltage around the ground rod could be as high as 120Vac.
The return path for the 120Vac ground fault current travels through the ground rod, through the earth, back to source, the Utility Power Company’s power transformer’s grounded neutral conductor. There are multiple paths provided through the earth for the ground fault current to travel back to the power transformer’s grounded neutral.
* Through the earth to the grounding electrode system of your home to the grounded neutral conductor in the electrical service equipment panel back to the source.
* Through the earth to the Utility Power Company’s driven ground rod at the transformer for connecting the neutral to earth.
* Through the earth to any of your neighbors grounding electrode systems to the grounded neutral conductor in the electrical service equipment panel back to the source.
.