Did electrician set up my dedicated subpanel correctly?


I’m green when it comes to all this stuff. I had my electrician set up 4x dedicated lines in a separate subpanel for my listening room. I also gave him 1x EP-2050EE to install and 4x EP-2750 ground filters for each dedicated line. From this subpanel I’m running 4x 10-2 w/g CRYO Romex to 4x Furutech GTX-D NCF(R) receptacles.

Does everything look okay to the experts here or does anything stand out? One Q I had was if each of the dedicated lines needs to be on the same side of the panel?

Thanks

 

Link to pic of subpanel:

 

Ag insider logo xs@2xbattbot

Yea, the 2x 15 amp is to power the EP-2050ee (SPD+Noise filter). The extra 20 amp is an unused spare. The orange cable is the cryo.

Confused what you mean it’s not dedicated, oldhvymec?

OK I got it, nice clean set up. It is dedicated and to a room not just a single or double run. Same way I did it. I use wall mount 220/40 AC units in the listening room. The AC is not in the same box I ran all 4 AC units in a separate 100 amp sub too. I like sub panels. I have one for every addition in my home. The new main is going in with the solar plug and sub panel.

I'm going with a trailer vs roof mount. The maintenance, batteries everything is easier.. Just plug and play. I don't have to worry about solar thieves either at a few of the place I go . On guy his whole cabin was moved solar in all 4 miles away.

Like I told him when I tracked it. I don't have to find every track just the next one.. YUP stole his whole cabin. How much time do you get for stealing a whole house? LOL

Enjoy.. 

The EP-2050ee is a parallel whole house surge protector, waveform corrector and power conditioner. Because it's parallel, it won't limit current. The EP-2750 ground  filter provides additional filtration of the safety ground for the dedicated audio circuits. I've done the same in my homes.

@battbot

 

The four 20A branch circuit breakers are installed on both Lines, legs. Two on L1 and two on L2.

What is the main 2 pole breaker ampere rating? I can’t read the number on the breaker handle.

Any idea the size of the feeder wires feeding the main 2 pole breaker? My guess is #6awg copper. If #4awg or larger the electrician would have installed a plastic bushing on the feeder box connector.

As for the installation and workmanship it looks good. I would have probably installed the EP-2050EE SPD straight across from the 2 pole breaker it connects to. The shorter the leads the better.

.

@jea48 Thanks for mentioning keeping the two black wires from the EP as short as possible. Recommended by the manufacturer for best results.