The EP-2050ee is a parallel whole house surge protector, waveform corrector and power conditioner. Because it's parallel, it won't limit current. The EP-2750 ground filter provides additional filtration of the safety ground for the dedicated audio circuits. I've done the same in my homes.
Did electrician set up my dedicated subpanel correctly?
I’m green when it comes to all this stuff. I had my electrician set up 4x dedicated lines in a separate subpanel for my listening room. I also gave him 1x EP-2050EE to install and 4x EP-2750 ground filters for each dedicated line. From this subpanel I’m running 4x 10-2 w/g CRYO Romex to 4x Furutech GTX-D NCF(R) receptacles.
Does everything look okay to the experts here or does anything stand out? One Q I had was if each of the dedicated lines needs to be on the same side of the panel?
Thanks
Link to pic of subpanel:
- ...
- 8 posts total
@
The four 20A branch circuit breakers are installed on both Lines, legs. Two on L1 and two on L2. What is the main 2 pole breaker ampere rating? I can’t read the number on the breaker handle. Any idea the size of the feeder wires feeding the main 2 pole breaker? My guess is #6awg copper. If #4awg or larger the electrician would have installed a plastic bushing on the feeder box connector. As for the installation and workmanship it looks good. I would have probably installed the EP-2050EE SPD straight across from the 2 pole breaker it connects to. The shorter the leads the better. . |
@jea48 Thanks for mentioning keeping the two black wires from the EP as short as possible. Recommended by the manufacturer for best results. |