One or two dedicated AC wire ?


Would it have a signeficant audible in performance between: FIRST- a dedicated AC wire for an audio stereo system connected to a power distribution bar with good AC cable and Furutech Duplex. SECOND- the same as first version, but adding another dedicated AC wire, and an other wall Furutech Duplex, to connect only the stereo power amp. Would I hear a significative improvement for the investement of time and electrical parts ?
audiosens
Post removed 

 

All three 20amp, 10 gauge Romex, and all three dedicated ground wire to new grounding rod,

Absolutely worthless and dangerous if the EGC (Equipment Grounding Conductors) are not also connected to the equipment ground bus bar in the electrical panel.

The earth does not possess some magical mystical power that that sucks nasties from audio equipment.

 

"Electromagnetic Compatibility Engineering" by Henry Ott

3.1.7 Grounding Myths

More myths exist relating to the field of grounding than any other area of electrical engineering. The more common of these are as follows:

1. The earth is a low-impedance path for ground current. False, the impedance of the earth is orders of magnitude greater than the impedance of a copper conductor.

2. The earth is an equipotential. False, this is clearly not true by the result of (1 above).

3. The impedance of a conductor is determined by its resistance. False, what happened to the concept of inductive reactance?

4. To operate with low noise, a circuit or system must be connected to an earth ground. False, because airplanes, satellites, cars and battery powered laptop computers all operate fine without a ground connection. As a mater of fact, an earth ground is more likely to be the cause of noise problem. More electronic system noise problems are resolved by removing (or isolating) a circuit from earth ground than by connecting it to earth ground.

5. To reduce noise, an electronic system should be connected to a separate “quiet ground” by using a separate, isolated ground rod. False, in addition to being untrue, this approach is dangerous and violates the requirements of the NEC (electrical code/rules).

6. An earth ground is unidirectional, with current only flowing into the ground. False, because current must flow in loops, any current that flows into the ground must also flow out of the ground somewhere else.

7. An isolated AC power receptacle is not grounded. False, the term “isolated” refers only to the method by which a receptacle is grounded, not if it is grounded.

8. A system designer can name ground conductors by the type of the current that they should carry (i.e., signal, power, lightning, digital, analog, quiet, noisy, etc.), and the electrons will comply and only flow in the appropriately designated conductors. Obviously false."

Henry W. Ott

 

.

 

.

.

 

I run 2 separate dedicated lines from a sub panel , the one line for my digital equipment uses Accustic Revive 10 g solid core in wall wire the other line uses 8 g solid core for my amp. Both have Furutech GTX R NCF duplexes.

I’ve always run separate dedicated lines , one for digital and one for the amp or amps.