jea48 said:
Where was your reference point used for the measurement? At the electrical panel?
ieales response:
Where else?
Usually the no load voltage is checked at the last outlet on the branch circuit. No loads are connected to the circuit. If a difference of potential, voltage is present it will be the same as the applied voltage at the feed end. In this case the branch circuit breaker to neutral bar voltage. If 120V at the panel it will measure 120V at the end of the branch circuit that has no load connected to it. (Add load and then measure again for VD.)
Why? Simple Ohms law. You need a load to have a VD. No load no VD. The internal resistance of a typical DMM is about 10M ohm.
jea48 said:
What type of volt meter did you use?
ieales response:
calibrated Fluke.
10M ohm internal resistance. 120V / 10M ohm = 0.000012 amp.
Jim
.