If arcing had occures and the lug and or neutral bar were burned and required replacement, this would constitute reconditioning.
"Reconditioning" defined by 2020 NEC, no.
Replace the interior with a new one yes. But not because of Nec 408.8 (A). Not the way I read it and the Art 100 definition of "Reconditioned" anyway...
I ran across this article doing a search. Actually I found a few articles on the subject that say the same thing.
I highly doubt you could purchase the lug and bar as individual items from Schneider.
Maybe the lug. Agree not the neutral rail bar. If the rail is burned/damaged the interior is toast. There is no repairing it.
I wonder if Schneider will pay for the labor to pull the old interior and install the new one? There will be several man hours involved. Add labor if the main breaker is in the panel. Electricians in my area cannot break the seal and pull the meter. Only the Utility Co. can pull the meter and reinstall it. Time is money...
Something that has not been mentioned in this thread or in the recall bulletin, other than a possible electrical fire inside the panel enclosure, is possible damage to 120V appliances and 120V electronic devices that are connected to the side with the bad neutral connection.
There will be a VD, (Voltage Drop), across an arcing loose connection. The greater the arcing the greater the VD. (Basically a resistance in series in the circuit.)
As you know only the unbalanced 120V L1 and L2 to neutral loads returns on the service neutral conductor to the utility power transformer neutral leg. The above arcing loose neutral connection is basically a loose service neutral connection between L1 and L2 connected 120 volt loads. The greater the imbalance of 120V L1 and L2 connected loads, connected to the neutral bar rail, the greater the voltage differences feeding the connected loads. Usually electronic device are fed over voltage and are damaged. As I am sure you already know.