I’m beginning to think you are just pulling my chain here...🤔
Where does the power that feeds your house come from?
A Utility Power Company?... Somewhere outside your House there is a step down power transformer that feeds power to the electrical service of your house...
Without a Single Phase 120/240V SPLIT PHASE power system there would be no 3 wire single phase multiwire branch circuit... Can’t have a 3 wire multiwire branch circuit without a split phase power system. The Utility Power Company’s step down power transformer’s center tapped 240V secondary winding is what creates the 120/240 split phase power system.
/ / / /
You asked Why?
Not sure why this would be happening.
jea48,
You say that, Zero amps will return on the shared neutral conductor to the source).
Not sure why this would be happening. And then from this point on in your response above I sort of lose an understanding of what you’re saying.
But I’m really trying to follow. And I think for many it would be nice to know the rationale here as well, as this is a very profound issue.
Remember This Post:
Jea48 said: (12-21-2022 at 08:46am)
A multiwire branch circuit is basically an extension of the split phase winding of the utility power transformer.
.