What a mess? Did you actually read the part where jea48 explained how your new work could easily be converted to one dedicated circuit in about 10 minutes? Then add a second one, and you're finished. You're out some additional money due to the first electrician not doing exactly what you asked. Stuff happens.
Wiring 2 outlets to 2 dedicated 20 amp circuits with a single 10/3 electrical wire.
Here's an idea (and it is code compliant), using one 10/3 romex electrical wire (three insulated conductors, and a bare ground wire - 10 gauge), you can wire two outlets to a double pole breaker (and yes the legs would not be the same, which on a quiet electrical system is not a big deal).
In this situation, 2 hot wires from the outlets would be wired directly to each of the circuit breakers, the neutral would be bridged between the two outlets and then connected to the appropriate spot on the panel, and the grounds for each outlet would be attached to the single ground wire that goes back to the panel. This would all appear within a quad outlet wall panel (ie. Two 20 amp outlets side-by-side)
For a long 70 foot run this seems prudent thing to do, less costly and kosher.
- ...
- 47 posts total
From a previous thread Jea was on, I would suspect the a quad is closer together than he would like the outlets to be? But cutting a new hole in the wall isn’t that big a deal. Or you could try using just one circuit for your gear and see what you think of that. |
@emergingsoul said:
Not exactly... Only the unbalanced 120V loads of L1 & L2 returns on the neutral conductor to the source. The balanced 120V loads of L1 & L2 are in series with one another and fed by 240V. Example: Say L1 120V load is 2 amps and L2 120V load is 6 amps. 2 amps is the balanced load. The difference of 6A minus 2A = 4A. 4A is the unbalanced load and returns on the neutral conductor to the source. The L1 120V 2A load represents digital equipment. The L2 120V 6A load represents a preamp and power amp. . |
JEA48..Help me with this ,please
Thanks in Advance! |
My three takeaways on this thread: One - to the layman electricity can be confusing and strange and yes electricity can do some unexpected or difficult to explain or even outright bizarre things in certain circumstances. Two - the layman that wants to understand a particular electrical question really needs some Electricity 101 before getting an in depth technical explanation. The layman has too many misconceptions and misunderstandings about electricity that need clearing away before technical explanations begin. The OP finally started to grasp the issue once he started to understand that split phase transformer that supplies the power to his house. Three - if the expert explains that choice A is not ideal and that choice B is the way to go, take his word for it. The recommendations byJEA48 in this thread are exactly what was done for my two dedicated power lines a few years ago. |