Power conditioner wire gauge? Serious issue


So I just figured out that all the 10 gauge wiring I have may be a problem if the power conditioner I use only uses 14 or 16 gauge wires to connect all those outlets you plug into in the back of those devices.

The specs are not part of the description when you buy Power conditioners.  Everybody recommends a dedicated 10 gauge wire from the panel but fails to consider what power conditioners use. 
 

Is this a serious problem? 

 

jumia

FEW people recommend 10 gauge wire from the panel.  Depends on the distance.

The main issue is resistance (R) per foot.  Here's the difference, per foot, at 72 degrees:

 

10:  0.00102 Ohms / foot

12: 0.00162 Ohms / foot

14:  0.00258 Ohms / foot

 

So running a 30' 10 gauge wire would be:

30 x 2 x 0.00102 = 0.0612 Ohms

Now, for the 6' of 12 gauge you want to run between the wall and your amp:

6 x 2 x 0.00162 =  0.0194

 

So the 6' of power cord is 1/3rd of the entire resistance. 

 

PS - We use 2x the distance because both the hot and neutral count.

OP: I think you need to stop thinking of 10 gauge as some magical ideal. It is not. It’s just better by immeasurably small amounts per foot and most 120V outlets will accept it. 

At 10 Amps of draw, the hypothetical 30’ 10 gauge wire would drop 0.6V vs. the 0.2V of the 6’ power cord. Tiny amounts relative to 120V incoming AC.

To answer your question, you will have no problem using smaller gauge with your 10 gauge wiring, don't worry about it.

Yes I know that i could use it  but I'm not concerned about that.

Seems to me that Power conditioners should be using 10 gauge wire internally. Dedicated outlets use 10 gauge wire so shouldn't the power conditioner outlets use them?

If you have a 10 gauge power cord connected to a power conditioner and then the individual outlets within the conditioner only use 14 or 16 gauge wire - to me that's a huge problem.

"Dedicated outlets use 10 gauge wire so shouldn't the power conditioner outlets use them?"

- This not the case in most homes systems, 10 ga. is overkill for all but the most demanding, high power amplifiers.

"to me that's a huge problem."

- Sorry if it is for you, but most would not see a problem. I suggest you don't use a power conditioner or replace the wiring inside with 10 ga.