Measurements for a dedicated line


The question of whether a homeowner should get a dedicated line is often like "should I get bangs." It’s a little complicated. Here are a couple of reasons to consider not:

I. My experience is that you won’t eliminate all the other noise coming from your home even if you do run a dedicated line. I still hear motors switching on and off despite being on completely different circuits.

II. A little resistance and a little inductance may actually be a good thing in keeping noise out of your line, so overkill on the wire gauge may not help this.

Why you definitely should get a dedicated line, with thicker wiring:

 

Less voltage sag.

 

Voltage sag means that under load the resistance in the line will cause the AC cabling int he wall itself to consume some of the AC voltage, giving your gear less volts to work with. This sag is proportional to current, so the more amps your gear is drawing the more sag.

This sag is something you can measure. There are two things you need to look: The hot to neutral voltage and the neutral to ground.

With nothing on the circuit your N-E (neutral to earth or ground) should be 2V or less. If it’s significantly higher than that stop and call an electrician. That’s true for any circuit in your home. High N-E values are indicators of a problem which may be in the circuit or in the service wiring from outside to the panel.

What happens when you turn your equipment on and play music is that the line will sag. The H-N (hot to neutral) voltage will drop, and the N-E will go up. Some sag as you turn on big amps is normal. So long as you are not tripping breakers you are fine. What you want to measure is the sag after your system has stabilized and while it’s playing music.

Keep an eye on the N-E value, as this will be a good indicator of the sag independent of the incoming line voltage. It may also point out where you may have issues. That is, if you measure an extra 2V of N-E, your sag is probably around 4V, so you went from 120V to 116V and you can be relatively comfortable it isn’t outside influences.

Of course, any good multimeter will work for this but I like plug in meters with built in N-E measurements. This one is cheap, and the N-E may not be hyper accurate, but it is the only device I’ve found on Amazon that will show you both the H-N and N-E voltages at the same time.

The nice thing about any plug-in type voltage meter is you can watch it over  a couple of days without hand holding probes in the socket.

If you find another which does both please post.

 

 

erik_squires

@dpop Those are certainly popular, and I believe the original.  There are now dozens of watt / voltage meters out there, with a variety of smart features, including wifi connectivity.  What I've yet to find is one that measures N-E at the same time as the V.  Still, being able to chart your V over a week can really help you understand your power issues.

Using the KAIWEETS KM117B Socket Tester (the one @erik_squires linked), I took some measurements around my home:

My pizza oven consumes 11.5 amps during operation (measured using my
Amprobe ACD-10 TRMS-PLUS meter). With the oven off, AC volts available at the outlet is 121.3 - 121.5. With the oven on, volts available at the outlet dropped to 117.8. N-E volts 00 with the oven on or off.

My microwave oven consumes 14.6 amps during operation (measured using the amprobe meter). Volts available at the outlet with the microwave off was between 121.3 - 121.5. Volts available at the outlet with the microwave on was 117.9. N-E volts 00 with the microwave on or off.

My main audio system is a 3 power amp tri-amped system. The power amps alone consume about 1.5 amps total powered on with no program material. AC volts at the outlet is 121.5 with the amps off. With the amps on, volts at the outlet are 121.0. Peak amps measured at loudest passage was 1.9 amps (or, 0.40 amps above powered up status). The feed is 15' of 10 AWG directly from the circuit breaker box. N-E volts was 00 with the amps on or off.

My furnace consumes 3.79 amps with the unit in full operation (gas burner heating, and forced air fan blowing). Volts available at the outlet with the furnace off was 121.5. Volts available with the furnace full on was 120.5. N-E volts was 00 with the furnace on or off. 

What this does prove to me is how important a dedicated run *is* for power amps, or high current consuming integrated amps or receivers. 

@dpop Excellent investigations!! :)  While I applaud your work, should also point out how few amps you are drawing is contributing to the stability of the voltage. Your wiring could handle 30 Amps, and you are drawing 2 at peak usage. 

Audiophiles should evaluate the potential benefits vs. costs.  The longer the circuit from the main panel, the more the power draw is, the more worthwhile a dedicated, large gauge circuit becomes.

@erik_squires Good point Erik. I have a Panini maker which is rather light in weight, and easier to relocate vs. my pizza oven or microwave. It consumes 11.8 amps (the pizza oven consumes 11.5 amps). I plugged it into my 10 AWG main audio feed AC outlet. Volts available at the outlet at that moment was 121.8. Volts available with the Panini maker on was 119.0 (a voltage drop of -2.8 volts). N-E volts was 00.

I knew the 10 AWG feed was about 15 feet in length from the circuit breaker box to the measuring point. My other AC circuit feeds for my microwave and pizza oven I discovered are on the same 20 amp circuit as each other (good thing I never have a reason to run the pizza oven and microwave at the same time). The pizza oven and microwave are on a completely different circuit than my 10 AWG AC feed. My house was built in 1942, and the pizza oven wiring has never been updated, except with a new outlet at some point. The microwave outlet was installed at a later date, with copper wiring. The previous owners of the house had that installed. It was tied into the same circuit as the pizza oven outlet. Within the past 10 years I updated that microwave/pizza oven circuit breaker to the recent AFCI type. I’m guessing the wire run to the pizza oven outlet is around 20 feet, and the microwave outlet is 30 feet. Suffice to say there was more voltage drop at the pizza oven outlet (consuming roughly the same amount of amps as the panini maker), at -3.7 volts, than there was at my dedicated 10 AWG feed (-2.8 volts), consuming roughly the same amount of current.

Some of this was eye-opening, as I didn’t anticipate I would see that amount of voltage drop with high current demand at my 10 AWG feed, only 15 feet away from the circuit breaker box. One thing is for sure, I would not want to have any audio components on a microwave or pizza oven circuit when they would be in use.

My house was built in 1942, and the pizza oven wiring has never been updated, except with a new outlet at some point.

@dpop

Ahhh! Yeah, you can’t do that today. The microwave gets it’s own circuit, which as of 2023 has to be CAFCI and GFCI protected.

Within the past 10 years I updated that microwave/pizza oven circuit breaker to the recent AFCI type.

Nice! Please make sure that all your kitchen counter top circuits are GFCI protected as well. Not sure if an outlet or updated breaker will be the most convenient for you in this case. Leave the fridge alone though, those trip GFCIs all the time. GFCI for kitchen counter top outlets has been code for decades but the latest 2023 NEC code expands GFCI to the dishwasher, microwave, and washer/dryer combos. I’m not sure you need to go that crazy, but I do think it’s worth the GFCI outlets on the counter tops for sure, and any outlets under a kitchen counter as well.

If you buy more GFCI outlets, any major brand but Leviton seem to have high trust factors with online electricians.