Here is a photo of an old 3 wire rubber/cloth covered wire, steel armored BX cable.
https://i.sstatic.net/pvjp6.jpg
I assume the outlet box that is now blanked off was the Hot 120Vac ground contact duplex receptacle outlet. I hope the electrician taped off or put wire nuts on the two conductors before he blanked off the outlet box. The outlet was the end of a branch circuit with several other wall outlets, and more than likely ceiling light fixture(s) a head of it.
I would suggest you buy this pair of voltage testers and check all the rest of the wall outlets in your apartment.
Use the non contact voltage tester to check for a Hot 120Vac ground contact. Any of those outlets are a possible electrical shock hazard. Put a piece of tape over the outlet so you will remember not to use it/them.
You might consider something like this to plug a power strip(s) into to feed all of your audio equipment. Feed everything from one duplex receptacle wall outlet. The total combined load amps of all the connected audio equipment is around 3 or 4 amps.
.