I m puzzle what is the difference between a PC with a 20amp IEC and one with 15amp IEC but same 15amp plug and drawing from the same circuit? Noticed most PC with 20amp IEC are sold with 15amp plug. Currently using a power amp which accepts only 20amp IEC. TQ you in advance
128x128audioblazer
Zieman, "if equipment needs 20amps feed it that". This is my confusion. I do knw that a 20amp wall plug can accept a 15am or 20amp plug. However, if an equipment needs 20amp IEC like my CJ350, why does most 20amp power cord comes with a 15amp plug? " Worry abt the home AC circuit"? If the wall plug is 15amp isnt that the max draw by the amp? is that is so isnt a 20amp IEC redundant? Pardon my confusing tq
Equipment manufacturers are starting to use 20amp IEC inlets on their gear because it is a more solid connection than the 15amp IEC.
First I would bet the cord is not listed by UL or any other recognized testing agency.

Under UL guidelines a NEMA 5-15P plug, (15 amp), cannot be connected to a continuous load of more than 12 amps.
A NEMA 5-20P plug a continuous load of more than 16 amps.

NEC allows 2 or more NEMA 5-15R (15 amp) receptacles to be connected to a 20 amp branch circuit. (A duplex receptacle is two). But because of the requirements placed on the NEMA 5-15P the continuous load should never be more than 12 amps. NEC also says the receptacle shall not have a continuous load of more than 12 amps placed upon it.
Remember many 15 amp convenience outlets, receptacles, are connected to 15 amp branch circuits. That's why a 20 amp plug will not plug into a 15 amp receptacle.....

Now to your equipment with an 20 amp IEC connector. I doubt it would ever draw more than 12 amps continuous load. Continuous load? 3 or more hours..... Check the data plate on the back of the unit. Usually rated in watts or VA. Divide by 120V that will give you amps.

Post removed 
Audioblazer I also have a cj350 and I use a PS Audio Statement Xtreme power cord. It has a 15 amp IEC so I use a 20IEC to 15IEC connector from voodoo audio (bought here on the Gon). I am using a 20 amp circuit to the amp with PS Audio Power Port recepticle (accepts 20 amps). Not sure this answers your question. Neither cj nor PS Audio felt there would be any issues with what I was doing. PS Audio didn't offer a pure 20 amp IEC end on their power cords at the time; don't know if they do now or not. PS Audio also commented that there would be no issues with connecting there power cord to a 20 amp circuit.