First I would bet the cord is not listed by UL or any other recognized testing agency.
Under UL guidelines a NEMA 5-15P plug, (15 amp), cannot be connected to a continuous load of more than 12 amps.
A NEMA 5-20P plug a continuous load of more than 16 amps.
NEC allows 2 or more NEMA 5-15R (15 amp) receptacles to be connected to a 20 amp branch circuit. (A duplex receptacle is two). But because of the requirements placed on the NEMA 5-15P the continuous load should never be more than 12 amps. NEC also says the receptacle shall not have a continuous load of more than 12 amps placed upon it.
Remember many 15 amp convenience outlets, receptacles, are connected to 15 amp branch circuits. That's why a 20 amp plug will not plug into a 15 amp receptacle.....
Now to your equipment with an 20 amp IEC connector. I doubt it would ever draw more than 12 amps continuous load. Continuous load? 3 or more hours..... Check the data plate on the back of the unit. Usually rated in watts or VA. Divide by 120V that will give you amps.
Under UL guidelines a NEMA 5-15P plug, (15 amp), cannot be connected to a continuous load of more than 12 amps.
A NEMA 5-20P plug a continuous load of more than 16 amps.
NEC allows 2 or more NEMA 5-15R (15 amp) receptacles to be connected to a 20 amp branch circuit. (A duplex receptacle is two). But because of the requirements placed on the NEMA 5-15P the continuous load should never be more than 12 amps. NEC also says the receptacle shall not have a continuous load of more than 12 amps placed upon it.
Remember many 15 amp convenience outlets, receptacles, are connected to 15 amp branch circuits. That's why a 20 amp plug will not plug into a 15 amp receptacle.....
Now to your equipment with an 20 amp IEC connector. I doubt it would ever draw more than 12 amps continuous load. Continuous load? 3 or more hours..... Check the data plate on the back of the unit. Usually rated in watts or VA. Divide by 120V that will give you amps.