I'm still not sure where this leaves us on the question of a separately derived power source or an isolated ground.
01-07-15: Jafreeman
The secondary of the isolation transformer of the Richard Gray RM PRO unit is a separately derived system. The RM PRO unit also provides surge protection on the line side of the primary winding.
Here is just a snippet from a book written by Henry Ott.
Quote.
"Basically, in the case of a separately derived system, we start all over again, as if it was the main service entrance panel and we create a new single point neutral to ground bond."
End of quote.
3.1.6 Separately Derived Systems, by Henry Ott.
>>>>>>>>>>>
What a shielded isolation transformer does.>>>>>>>>
EXACTPOWER, PDF Page 10
Quote.
"| "Residential Power Distribution & Grounding -
The Truth
In residential installations, a dedicated electrostatically shielded isolation transformer will act as a buffer
between the utility company electrical system and the protected electronics systems such as AV equipment,
home theater electronics, automation systems, and data devices. These isolation transformers must be
hard-wired by a licensed electrician.
This transformer, when correctly installed, is an effective sink for the collective ground leakage current of
multiple switch-mode power supplies found in almost all modern equipment. The AV and control system will
benefit from the improved power quality, greatly reducing the effects of ground loops through having a single
point source for power and grounding.
An isolation transformer is a device that prevents power quality problems by galvanically isolating the load
from the power source, and incorporates a new neutral conductor that is bonded to a newly derived system
ground. This newly derived neutral to ground bond eliminates common-mode voltages at that point, which
are usually the main cause of unreliable system operation, equipment failure and service calls."
End of quote.
I suggest you start reading from page 8.
>>>>>>>>>>
The 1200 is the best item for an entire front end.
What are you plugging the 1200 into? The RM PRO unit?
>>>>>>>>>
As for an isolated ground not sure what you are referring to. If you mean an isolated ground for bonding the new neutral of the secondary of an isolation transformer that is a No No. The neutral must bond, connect, to the main electrical service grounding system of your home. The neutral bond, connection, in your case is made through the safety equipment grounding conductor of your 10-2 with ground branch circuit wiring that feeds the isolation transformer. Another good reason you used #10 wire for the branch circuit.
.