Subaruguru,
The Belden 83802 is a FPLP rated cable, power-limited fire alarm plenum cable. FPLP cables are listed in NEC 760, National Electric Code:
"Conductor and cables for power-limited fire alarm circuits shall be listed for the purpose and meet the following requirements: A. Conductors are solid or stranded copper. B. Conductors in a multiconductor cable shall not be smaller than 26 AWG. Single conductors shall not be smaller than 18 AWG. C. The voltage rating shall not be marked on the cable. Voltage ratings marked on the cables may be misinterpreted to suggest that they can be used for Class 1, electric light and power applications. ..."
That seems to infer the Belden 83803/2 is NOT approved for use in normal household AC circuits. You should check with the local electrical inspector if the NEC is adopted in your area before going any further with this and advise others to do the same.
Romex NM, the typical wire used in AC circuits, is not approved in plenums because the jacket will melt creating toxic gases when the heat from a fire moves through the ducts. The teflon insulation and jacket on the plenum cable is more resistant to the heat.
Romex NM has a max voltage rating of 600v and 83803 is rated at 300v.
JPS Labs makes in-wall wire that is 600v rated like Romex NM. It is very expensive at $18/ft., but doesn't compromise the safety and is designed for what you want to do.
Power AC In-Wall cable