Help My AC line voltage is 128V


I have recently tested the line voltage reading out from my AC lines. They read 128V ! Knowing that 128V is almost 10% more than the standard 117V and most components inside the equipments have a 5% tolerance only. Would this unusual high voltage damage my equipments? Even though I have all my stuffs hooked onto a delicated line but when my wife uses the washing machine, the power reading jump slight up and down... This is a power spike at a high 128V... Sounds dangerous to me... I now have a habit of unplugging them everytime I finished and I am getting frustrated at this. Will getting a voltage stabilizer help? PS Audio P600 or the Monster Cable stuff?
infinity_audio
Power companies deliver voltages from 114 to 126 volts, which is the accepted tolerance. The higher voltages are delivered when transmission line lossed are expected so that the customer furthest away will get 120 volts or so. Also, the utility voltage is RMS - which means that at 120 volts you receive peak voltages of 170 volts. If your voltage meter is not a true RMS type, then the readings you get may not be reliable.

The best thing to do is contact the utility and express in no uncertain terms you have high voltage and are concerned. Let them make the call - as they are ultimately liable and responsible. I would also call an electrician who knows the area and see if what you have is common in the neighborhood.

An true overvoltage condition is above 132 volts rms for an extended period. This level will most likely do damage to sensitive electronics. But most electrical equipment with UL ratings are designed to operate within an accepted utilization voltage range of 104 to 127 volts. I wouldn't say 128v is not a dangerous situation - but one of concern that should be checked out by the utility or an electrician to make sure there's nothing other than utility-derived overvoltage.
Yeah, what GS said. I had the same situation and the power company retapped the transformer on the pole outside my house to bring it down.
Oh so 128V is pretty usual thing in some area because at least Herman had the comapny turned it down for him. My light bulbs in my house keep blowing and this is getting ridicurous! I spend almost $10.00 on light bulbs every 3-5 months! At least 1 light bulb blows in every 2-4 weeks! I suspect the spike kills them all the time. I will try to contact ConEd to either "show me" that it's is okay or tapped down the trans. like what they did to Hermans' neighborhood.