UPgradeing dedicated line components


Six months ago I installed 3 dedicated lines for audio. One to amp, one to preamp, and one to digital. I used standard solid core 10ga romex for amp and 12 ga otherwise. I have a Square D box with distance to outlets not more than 20'. Used hospital grade outlets, however inexpensive ones.

I seek input on value of:
1) Upgrading the breakers in the square D box.
2) Replacing the romex for 10ga stranded cable for all lines.
3) Upgrading the outlets to PS audio or something of ~equal value.

Thanks in advance for any thoughts. Mike
mesch
I seek input on value of:
1) Upgrading the breakers in the square D box.
2) Replacing the romex for 10ga stranded cable for all lines.
3) Upgrading the outlets to PS audio or something of ~equal value.
#1) There is no upgrading the breakers. Hopefully you have a Square D QO panel and not the Homeline series.
QO has copper plated bus, Homeline has aluminum bus.

All three dedicated branch circuits should be fed from the same Line, leg, of the panel.

#2) #12 wire is plenty big for the preamp and digital for a 20' run. You will not hear any difference changing them out to #10. (I would not use stranded wire)

#3) I can't help you there. I will tell you all hospital grade recepts are not created equal. I am using the Hubbell 8300H hospital grade non plated contacts with a non plated brass backstrap. The recepts are cryoed.

Stay away from recepts that use nickel plating on the contacts and the mounting backstrap. Also you do not want a recept that has a ferrous steel backstrap.