advice on dedicated line


Hello.

I need to have an electrician do some work on my house, and am mulling over a dedicated line for my sound system while she or he is there.

I am new to this, though, and not especially sophisticated about electrical matters. So I am wondering what exactly I want to ask for, and thought maybe you all would know.

I have an amplifier, a cd player, a Sonos unit, and a DAC.

Do I want two dedicated lines--one for the amplifier and one for everything else? So 2 20 amp circuits with 10 gauge wire?

Do I need to say something else about ground wires etc? About the breaker box?

Can I get 3 outlets on one dedicated line?

What kind of outlets do I want?

Anything else I should know?

Thanks!

mc
mcanaday
I live in philly in a neighborhood that runs off the same transformer and we're prone to lightening strikes. Even with my modest system I use a Furman Pro pwr strip for my Sunfire amp, but as Al stated, effect on SQ is system dependent. There have been more than a few nites where I've lost power and heard the breakers on the surge protectors click off. You have an awesome amp, Bifwynne and its worth trying one.
FWIW I like the design of the Brickwall with it's isolated receptacles
Uuuuhhm, maybe the most effectice "surge protector" for my amp is to simply pull the plug when not in use, and not to use my stereo during storms. The other gear is surge protected, if such devices even work.
Here's a question to all you knowledgeable folks...Its been mentioned many times to have the digital components on their own dedicated line; now I'm assuming this means a transport cabled to an external DAC or a hard drive setup.

Why is it recommended not to share the same AC line as analogue components?
Secondly, is a surge protector using isolated receptacles an alternative?
Thanks.
Its been mentioned many times to have the digital components on their own dedicated line.... Why is it recommended not to share the same AC line as analogue components?
The most significant generators of electrical noise in most systems are components containing substantial amounts of digital circuitry, and power amplifiers. Some of that noise will be fed back into the power cord of the component which generates it, from where it will to some degree propagate through the power wiring to analog components, with unpredictable but potentially perceptible adverse sonic effects.

Everything else being equal, the longer the wiring path is between the power cords of noise generating components and components that may be susceptible to that noise, the more that noise will be attenuated. The most significant reason for that perhaps being the inductance of the wiring. The inductance of wiring is proportional to length. A given amount of inductance presents an impedance which is proportional to frequency. Electrical noise generated by digital circuitry tends to be at very high frequencies, and therefore can be significantly attenuated by the inductance of a substantial length of wire.
Secondly, is a surge protector using isolated receptacles an alternative?
It's certainly an alternative to consider and/or try, and in fact that's what I do with my CDP, which is the one digital component in my system. How that approach would compare with having a digital component on a separate dedicated line can't be predicted with any certainty, as it would depend on many unpredictable and unknown variables, including the technical characteristics of the noise generated by the particular digital component, how the particular analog components would react to that noise, the characteristics of the filtering that is provided between receptacles, and the susceptibility of the particular components to ground loop issues if they were to be put on separate dedicated lines.

Best regards,
-- Al
Elizabeth is correct,,,there is really no need for more than one 20 amp line and you are looking for grounding issues otherwiseÂ…even some manufacturers discourage it